Florida State University Search
Active Building Code Administration Project Inspection Results

BCA Project #: 25-03700- Westcott -0001 Rooms 0313Q & 0315 Modifications
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2026/03/24 | Electrical | Wall Rough-in | Conditional | Rocky Wilde | This is a partial rough in for electrical in room 315 juction box behind wall needs to be accessible, deleted boxes and conduit needs to be removed, open conduit needs to be capped, label juction boxes, |
| 2026/03/24 | Electrical | Ceiling Rough-in | Conditional | Rocky Wilde | This is a partial rough in for electrical in room 315 see wall rough |
| 2026/03/24 | Building/Structural | Framing | Failed | Kody Boswell | This is a partial rough in for electrical in room 315 additional anchors required |

BCA Project #: 25-03695- Alumni Ctr Fac - 0465 Renovate RM 145
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2025/12/17 | Building/Structural | Final Building | Partial | Rocky Wilde | TCO inspection for conclusion of Phase 1, closet areas are closed off unable to inspect the elctrical. |
| 2025/12/17 | Building/Structural | Final Building | Partial | Rocky Wilde | TCO inspection for conclusion of Phase 1 |
| 2025/12/17 | Building/Structural | Final Building | Partial | Paul Nitz | TCO inspection for conclusion of Phase 1 |
| 2025/11/19 | Electrical | Ceiling Rough-in | Partial | Rocky Wilde | |
| 2025/10/30 | Building/Structural | Sheetrock | Conditional | Kody Boswell | Reviewed interior sheathing attachment to LG framing. Result is condtional pending receipt of photos from the Contractort showing screws were added in two areas that were missing at the time of inspection. |
| 2025/10/28 | Building/Structural | Framing | Conditional | Paul Nitz | framing pics |
| 2025/10/28 | Electrical | Wall Rough-in | Passed | Rocky Wilde |

BCA Project #: 25-03692- Howser Stadium Upgrade Ph 2
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2026/06/17 | Building/Structural | Final Building | Cancelled | Paul Nitz | |
| 2026/06/17 | Mechanical | Final Mechanical | Conditional | Paul Nitz | 1) Final Test and Balance has not been submitted 2) UV protectant will be required on the exterior condensation line |
| 2026/06/17 | Electrical | Final Electrical | Passed | Rocky Wilde | |
| 2026/02/18 | Building/Structural | Final Building | Failed | Rocky Wilde | 1) Minimum breaker for HVAC condensing units A & B is 20.8 as per the manufacture’s information plate 2) Plenum seal is damaged and dented due to people walking on it in the mechanical room 3) Check specs for condensation insulation to be protected with an aluminum jacket 4) An additional support will be required for the condensation line in the mechanical room 5) Please have the HVAC contractor state why the emergency shut off for the unit didn’t activate when the unit’s condensation drain was overfilling with water 6) Condensation units or disconnects for the units need to be labeled 7) Disconnect for the condensation unit needs to be accessible 8) An engineered letter needs to be provided for the flashing detail around the windows that was changed as well as for the framing and waterproofing that was not inspected 9) All new junction boxes need to labeled 10) Raceway and tray need to be bonded If you have any questions, please just me know Paul |
| 2025/10/07 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for sidewalk pour back |
| 2025/09/30 | Building/Structural | Structural | Failed | Paul Nitz | Window/storefront installation 1) fasteners were required to be 1/4" min per manufacturers installation instructions and they were using 3/16". |
| 2025/09/26 | Building/Structural | Structural | Failed | Paul Nitz | Not ready |
| 2025/09/25 | Mechanical | Duct Rough-in | Conditional | Paul Nitz | 1) round duct 19"-24" require (2) 10ga wire for support. SMACNA 5-2 2) plans need to reflect the change of location of the condensing/heat pump units by CO |
| 2025/09/17 | Electrical | Wall Rough-in | Passed | Rocky Wilde | |
| 2025/09/16 | Building/Structural | Sheetrock | Passed | Paul Nitz | this inspection was completed on 9/16/25. the inspection was for both sheetrock and plywood. This does not include the plywood for the IT room. That will be furnished by the IT team |
| 2025/09/12 | Electrical | Wall Rough-in | Passed | Rocky Wilde | |
| 2025/09/10 | Building/Structural | Insulation | Passed | Paul Nitz | |
| 2025/09/09 | Building/Structural | Re-Inspection | Passed | Paul Nitz | |
| 2025/09/08 | Building/Structural | Framing | Cancelled | Paul Nitz | |
| 2025/09/08 | Mechanical | Duct Rough-in | Passed | Paul Nitz | |
| 2025/09/04 | Building/Structural | Framing | Failed | Paul Nitz | 1) Studs missing 2) Screws missing 3) Bracing (blocking) missing for dens glass |
| 2025/09/04 | Building/Structural | Sheetrock | Failed | Paul Nitz | Georgia Pacific installation instructions call for a 6 & 8 screw pattern for structural dens glass panels |
| 2025/08/28 | Electrical | Underground | Passed | Rocky Wilde | |
| 2025/08/15 | Building/Structural | Framing | Failed | Kody Boswell | Reviewed LG framing for new exterior infill walls. The following needs to be corrected or addressed: 1) It's unclear where bracing and blocking should be installed. Half points of vertical studs? Third points of vertical studs? Contractor to get clarification from EOR. 2) Top and bottom continuous track doesn't have the required fastener spacing per structural drawings. Contractor to install fasteners at 6" OC 3) Double vertical studs are required at new window jamb locations. They were not in place at time of inspection. Contractor to install vertical studs as needed. 4) Additional connections at interior door headers for IT and mech room are to be installed. |
| Building/Structural | Final Building | Conditional | Rocky Wilde | Reinspection….BCA punch list items see mep | |
| Electrical | Final Electrical | Conditional | Rocky Wilde | Reinspection….BCA punch list items juction box labeling incomplete, bonding at cable tray incomplete, | |
| Mechanical | Final Mechanical | Conditional | Rocky Wilde | Reinspection….BCA punch list items plenum needs to be fixes from dents |

BCA Project #: 24-03684-D FSU Lacrosse Facility - Press Box/Concessions
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2026/03/27 | Building/Structural | Re-Inspection | Passed | Kody Boswell | TCO for 3/29/26 game day. |
| 2026/03/13 | Building/Structural | Re-Inspection | Conditional | Rocky Wilde | TCO for Game Day bon 3/14/26 |
| 2026/02/23 | Building/Structural | Re-Inspection | Passed | Rocky Wilde | Event TCO for Press Box |
| 2026/02/23 | Building/Structural | Final Building | Passed | Rocky Wilde | Event TCO for Press Box |
| 2026/02/20 | Electrical | Ceiling Rough-in | Passed | Rocky Wilde | re-inspection Bathroom E Rough at PM interior. |
| 2026/02/20 | Electrical | Re-Inspection | Passed | Rocky Wilde | re-inspection Bathroom E Rough at PM interior. |
| 2026/02/19 | Electrical | Ceiling Rough-in | Passed | Rocky Wilde | Hard lid E rough at bathroom of PB |
| 2026/02/16 | Mechanical | Wall & Ceiling | Passed | Paul Nitz | Above ceiling Mechanical only... |
| 2026/02/16 | Electrical | Ceiling Rough-in | Passed | Rocky Wilde | E rough for hard ceiling cover. 2- exterior soffits 2 interior soffits |
| 2026/02/12 | Building/Structural | Sheetrock | Passed | Paul Nitz | Screw inspection for sheetrock mud. Press Box |
| 2026/02/12 | Building/Structural | Framing | Passed | Paul Nitz | Couple of walls in PB back side corridor |
| 2026/02/12 | Electrical | Final Electrical | Passed | Rocky Wilde | Temp Clubhouse Double wide. Power panel connect. |
| 2026/02/06 | Building/Structural | Final Building | Partial | Rocky Wilde | Temp TCO for Press Box. |
| 2026/02/03 | Building/Structural | Sheetrock | Passed | Kody Boswell | Screw inspection second side. |
| 2026/02/02 | Electrical | Underground | Passed | Rocky Wilde | requested post cable pull inspection |
| 2026/01/30 | Building/Structural | Re-Inspection | Passed | Kody Boswell | Reviewed LG framing for exterior soffits |
| 2026/01/30 | Building/Structural | Framing | Conditional | Kody Boswell | Reviewed LG framing for interior wall framing for press box corridor and rooms. Result is conditional pending repairs in several areas. Repairs required include repair to wall bracing that was cut and several vertical studs that had been cut by other trades. |
| 2026/01/30 | Building/Structural | Re-Inspection | Passed | Kody Boswell | Reviewed LG framing for restrooms |
| 2026/01/30 | Building/Structural | Framing | Passed | Kody Boswell | Reviewed LG framing for restrooms |
| 2026/01/30 | Electrical | Wall Rough-in | Passed | Rocky Wilde | |
| 2026/01/30 | Building/Structural | Wall/Ceiling | Passed | Rocky Wilde | reinspection restrooms |
| 2026/01/30 | Building/Structural | Re-Inspection | Passed | Kody Boswell | Reinspect ADA balcony at stadium seating. 10 am concrete |
| 2026/01/30 | Building/Structural | Slab | Passed | Kody Boswell | Reinspect ADA balcony at stadium seating. 10 am concrete |
| 2026/01/30 | Electrical | Wall Rough-in | Passed | Rocky Wilde | |
| 2026/01/30 | Building/Structural | Framing | Passed | Kody Boswell | Reviewed framing for exterior soffits |
| 2026/01/30 | Building/Structural | Re-Inspection | Passed | Rocky Wilde | reinspection restrooms |
| 2026/01/29 | Mechanical | Duct Pressure Test | Passed | Paul Nitz | Press Box 1) This was for a pressure test on the main trunk line. A rough mechanical will still be required for the system. |
| 2026/01/29 | Building/Structural | Slab | Failed | Paul Nitz | stadium seating at PB 1) This inspection was for the press box handy cap seating area, steps and right and left side of the handy cap area. The right and left side of the handy cap seating are as well as the steps passed inspection. An engineered letter will be required for the 3” non reinforced “cold joint” section in front of the handy cap area. |
| 2026/01/27 | Building/Structural | Framing | Failed | Paul Nitz | Frame for PB / Screw insection for restroom sheetrock 1) issues not addressed from the last inspection |
| 2026/01/26 | Building/Structural | Slab | Passed | Paul Nitz | Press Box stadium seating for ramp landing support. 1) this was for the left and right side only, the landing was not formed up |
| 2026/01/26 | Building/Structural | Slab | Passed | Paul Nitz | Stadium Seating next to last pour |
| 2026/01/26 | Building/Structural | Framing | Passed | Paul Nitz | Restrooms / Server room 1) this was for the restrooms only, the server room was not compelte |
| 2026/01/26 | Plumbing | Rough-in | Passed | Paul Nitz | Interior bathroom at Press box |
| 2026/01/23 | Electrical | Final Electrical | Passed | Rocky Wilde | Temp Trailer Clubhouse |
| 2026/01/23 | Building/Structural | Framing | Partial | Paul Nitz | Interior metal stud restrooms only 1) mens and women restroom back wall only |
| 2026/01/23 | Building/Structural | Roofing | Passed | Rocky Wilde | Roof Roof |
| 2026/01/23 | Building/Structural | Framing | Partial | Paul Nitz | Frame for restrooms / Frame for server room. At Press Box. 1) mens and women restroom back wall only |
| 2026/01/22 | Building/Structural | Slab | Passed | Rocky Wilde | Another round of stadium seating concrete. |
| 2026/01/22 | Passed | Paul Nitz | MEP pipe insulation inspection for cover. Restrooms / Janitors closet / Grab and Go only PB Restroom only. 1) this was for the insulation, press box mens and womens bathroom in wall | ||
| 2026/01/21 | Building/Structural | Structural | Passed | Kody Boswell | Reviewed reinforcing steel for the fourth row of spectator seating |
| 2026/01/21 | Building/Structural | Roofing | Passed | Kody Boswell | In-progress roofing inspection for the flat roof area. Contractor was in the process of mechanically fastening coverboard over insulation, secured to the structural steel deck below. |
| 2026/01/20 | Plumbing | Rough-in | NOT READY | Paul Nitz | Cover insp for PB restrooms |
| 2026/01/20 | Building/Structural | Structural | Passed | Kody Boswell | Reviewed steel roof deck attachment to steel structure for the flat roof area and two sloped roof areas. Sloped roof areas were covered with membrane so review was performed from the ground. |
| 2026/01/20 | Plumbing | Rough-in | Passed | Paul Nitz | Mens and PB restrooms. |
| 2026/01/20 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for the thrid row of seating |
| 2026/01/20 | Plumbing | Rough-in | NOT READY | Paul Nitz | Cover insp for PB restrooms |
| 2026/01/16 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for the second row of stadium seating |
| 2026/01/15 | Plumbing | Storm Piping & Test | Passed | Paul Nitz | UG civil stormwater pipe. |
| 2026/01/15 | Plumbing | Water Piping & Test | Passed | Paul Nitz | Civil DOM water pressure test |
| 2026/01/14 | Building/Structural | Slab | Conditional | Kody Boswell | Reviewed reinforcing steel for the bottom row of stadium seating. There were a few areas with insufficient bottom cover of rebar to grade below. There were also 2 missing longitudinal bars located at the bottom of each side of the trench drain. Result is conditional pending the above items are corrected/installed. Contractor was in the process of installing missing rebar and correcting cover issues as FSU BCA left the site. |
| 2026/01/13 | Plumbing | Rough-in | Passed | Paul Nitz | Womens restroom at Press Box |
| 2026/01/12 | Plumbing | Storm Piping & Test | Passed | Paul Nitz | Stormwater pipe at back of Clubhouse |
| 2026/01/09 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for the exterior SOG at the sout side plaza seating area |
| 2026/01/08 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for SOG located at the north exterior recreational seating area |
| 2026/01/07 | Plumbing | Underground | Passed | Paul Nitz | |
| 2026/01/07 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for 4 ramps |
| 2026/01/06 | Plumbing | Underground | Passed | Paul Nitz | |
| 2025/12/30 | Fire Safety | Fire Water Underground | Passed | Rocky Wilde | Flush and Hydro of 8" underground Fire Main and 3 Fire Hydrants. |
| 2025/12/23 | Building/Structural | Masonry | Passed | Rocky Wilde | Masonry wall rebar 3 rd lift |
| 2025/12/22 | Building/Structural | Masonry | Passed | Rocky Wilde | |
| 2025/12/19 | Plumbing | Underground | Passed | Paul Nitz | |
| 2025/12/19 | Plumbing | Underground | Passed | Paul Nitz | |
| 2025/12/19 | Plumbing | Underground | Passed | Paul Nitz | |
| 2025/12/17 | Plumbing | Underground | Passed | Paul Nitz | |
| 2025/12/17 | Building/Structural | Masonry | Conditional | Kody Boswell | Reviewed reinforcing steel for the 3rd lift for CMU walls above floor level. Result is conditional pending the following: 1) Sawcutting of bond beam after grout has cured for one interior wall. During inspection it was observed that bond beam reinforcing ran continuous over a vertical control joint, which is not in compliance with masonry typical details. 2) Missing vertical bars are installed. Only a few locations had missing reinforcing. This was discussed with the contractor prior to FSU BCA leaving the job site. Contractor was in the process of installing missing vertical reinforcing as FSU BCA left the site. |
| 2025/12/16 | Plumbing | Underground | Failed | Paul Nitz | 1) Slope not met for the storm drain |
| 2025/12/16 | Building/Structural | Re-Inspection | Passed | Paul Nitz | Reinspection |
| 2025/12/12 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for the interior SOG for the clubhouse. |
| 2025/12/10 | Plumbing | Storm Piping & Test | Passed | Paul Nitz | backside of Press Box stormwater pipe. |
| 2025/12/10 | Building/Structural | Masonry | Conditional | Kody Boswell | Reviewed reinforcing steel for the 2nd lift for CMU walls above floor level. Result is conditional pending receipt of photos of showing additional vertical reinforcing has been added where lap splice lengths were too short. This was discussed with the Contractor while on site. Photos were received by the Contractor after FSU BCA left the site. |
| 2025/12/09 | Building/Structural | Masonry | NOT READY | Kody Boswell | CMU infill at LAX Press Box Cleanout holes in block containing vertical reinforcing were not cut (8 ft lift) and there were some walls with no access (scaffolding) to look down into reinforced cells |
| 2025/12/09 | Plumbing | Storm Piping & Test | Passed | Paul Nitz | UG Civil UP stormwater at the Press box. |
| 2025/12/04 | Plumbing | Underground | Passed | Paul Nitz | |
| 2025/12/03 | Plumbing | Underground | Passed | Paul Nitz | |
| 2025/12/02 | Plumbing | Underground | Passed | Paul Nitz | |
| 2025/11/25 | Building/Structural | Masonry | Conditional | Kody Boswell | Reviewed reinforcing steel for the 1st lift for CMU walls above floor level. Result is conditional pending recepit of video/photos of masonry sills at pressbox windows being cleaned out. There was excessive mortar in a few locations. Video and photos were received by the Contractor after FSU BCA left the site. |
| 2025/11/20 | Plumbing | Underground | NOT READY | Paul Nitz | more civil |
| 2025/11/19 | Plumbing | Underground | Passed | paul nitz | |
| 2025/11/18 | Plumbing | Underground | Passed | Paul Nitz | |
| 2025/11/18 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for portions of the slab on grade. Areas reviewed include the pressbox interior slab and exterior covered seating on both side of the building. |
| 2025/11/13 | Plumbing | Underground | Passed | Paul Nitz | Fire water |
| 2025/11/12 | Plumbing | Underground | Passed | Paul Nitz | FOR THE CLUBHOUSE. |
| 2025/11/12 | Plumbing | Underground | Passed | Paul Nitz | |
| 2025/11/12 | Plumbing | Underground | Passed | Paul Nitz | Civil Storm water insp |
| 2025/11/06 | Building/Structural | Masonry | Passed | Rocky Wilde | Stem wall insp at PB and Clubhouse. |
| 2025/11/06 | Plumbing | Underground | Passed | Rocky Wilde | Stormwater continues |
| 2025/11/04 | Plumbing | Underground | Passed | Paul Nitz | Stormwater pipe and structure. LAX |
| 2025/11/04 | Building/Structural | Structural | Passed | Paul Nitz | Stormwater pipe and structure. LAX |
| 2025/10/31 | Building/Structural | Structural | Passed | Kody Boswell | Reviewed reinforcing steel for tie columns at the intersection of grids A-3 and A-6 |
| 2025/10/31 | Plumbing | Underground | Passed | Paul Nitz | This request is taking the place of the 1 pm request. Thank you. Press Box UG plumbing for cover |
| 2025/10/31 | Plumbing | Underground | Passed | Paul Nitz | Press Box UG plumbing for cover |
| 2025/10/30 | Building/Structural | Structural | Passed | Kody Boswell | Reviewed reinforcing steel for 2 tie columns (TC-2) |
| 2025/10/30 | Plumbing | Underground | Passed | Paul Nitz | Thanks |
| 2025/10/29 | Building/Structural | Masonry | Passed | Kody Boswell | Reviewed reinforcing steel for the 1st lift of CMU walls at the press box. 1st lift went from top of foundations to top of floor slab. All of the 1st lift is below grade and to be grouted soild. |
| 2025/10/29 | Plumbing | Specialty Piping | Passed | Paul Nitz | CIVIL Sanitation Pipe for cover. |
| 2025/10/28 | Building/Structural | Masonry | Failed | Paul Nitz | Stem walls LAX 1) Rocky and I visited the job site two times on 10/28 and both times they were not ready in addition to legible plans not being on site. |
| 2025/10/23 | Plumbing | Specialty Piping | Passed | Rocky Wilde | civil retaining wall ug drainage cover. |
| 2025/10/06 | Building/Structural | Wall/Ceiling | Passed | Kody Boswell | FSU BCA reviewed reinforcing steel for the field retaining wall on the Press Box side. Reinforcing steel was in substantial compliance with the contract documents. |
| 2025/10/06 | Building/Structural | Footing | Passed | Kody Boswell | Reviewed reinforcing steel for some Pressbox foundations. As discussed on site, the Press Box foundations inspection has passed with the understanding the following conditions/items are addressed: - Finish installing vertical wall dowels for exterior walls at 2’ on center. This was almost completed before I left the job site. - Adjust footing step formwork at one WF3.0 location. This was a work in progress when I left the job site. - Maintain 3” bottom and side cover for reinforcing steel. There were a few locations that didn’t have required cover. This was a work in progress when I left the job site. |
| 2025/09/15 | Building/Structural | Footing | Passed | Kody Boswell | Reviewed reinforcing steel for the field wall foundation (WF3.5) on the pressbox side. Reinbforcing steel was in substantial compliance with the contract documents. |
| Building/Structural | Re-Inspection | Rocky Wilde | Temp TCO for Game day on 3/8/26 | ||
| Building/Structural | Slab | Postponed | Kody Boswell | stadium seating at PB Contractor contacted FSU BCA prior to site arrival to postpone inspection to a later date due to cold weather. | |
| Plumbing | Specialty Piping | Paul Nitz | CIVIL Sanitation Pipe for cover. | ||
| Building/Structural | Structural | Cancelled | Kody Boswell | Contractor called to cancel inspection for concrete tie beams and tie columns prior to FSU BCA arriving on site | |
| Building/Structural | Masonry | Postponed | Kody Boswell | Contractor contacted FSU BCA prior to site arrival to cancel/postpone inspection due to weather | |
| Building/Structural | Masonry | Cancelled | Kody Boswell | ||
| Building/Structural | Re-Inspection | Rocky Wilde | Game Day TCO for Sunday game. |

BCA Project #: 24-03684-C FSU Lacrosse - Clubhouse
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2026/06/22 | Fire Safety | Fire Alarm Rough-In | Passed | James Melvin | |
| 2026/06/22 | Mechanical | Wall & Ceiling | Passed | Paul Nitz | |
| 2026/06/22 | Electrical | Ceiling Rough-in | Passed | James Melvin | |
| 2026/06/17 | Mechanical | Wall & Ceiling | Failed | Paul Nitz | 1) This is for above ceiling inspection 1) Mechanical strap needs to be replaced 2) Mechanical ducts need to be labeled |
| 2026/06/17 | Building/Structural | Wall/Ceiling | Conditional | Paul Nitz | 1) This is for above ceiling inspection 1) electrical was not ready |
| 2026/06/17 | Plumbing | Rough-in | Passed | Paul Nitz | 1) This is for above ceiling inspection |
| 2026/06/17 | Electrical | Ceiling Rough-in | Conditional | James Melvin | 1) This is for above ceiling inspection 1) electrical was not ready |
| 2026/05/28 | Building/Structural | Framing | Paul Nitz | 1)above ceiling inspection before the hard lid is installed and framing for sheetrock | |
| 2026/05/28 | Plumbing | Rough-in | Failed | Paul Nitz | 1)above ceiling inspection before the hard lid is installed and framing for sheetrock 1) pipe labeling is missing 2) saddle supports are missing |
| 2026/05/28 | Electrical | Ceiling Rough-in | Passed | Paul Nitz | 1)above ceiling inspection before the hard lid is installed and framing for sheetrock |
| 2026/05/28 | Building/Structural | Framing | Passed | Paul Nitz | 1)above ceiling inspection before the hard lid is installed and framing for sheetrock |
| 2026/05/28 | Mechanical | Duct Rough-in | Failed | Paul Nitz | 1)above ceiling inspection before the hard lid is installed and framing for sheetrock 1) supply, exhaust and return labeling is missing |
| 2026/05/27 | Electrical | Service Release | Passed | Rocky Wilde | |
| 2026/05/20 | Plumbing | Re-Inspection | Passed | Paul Nitz | Mech yard for HVAC Unit / Water heater re-work |
| 2026/05/20 | Plumbing | Gas Piping & Test | Passed | Paul Nitz | Mech yard for HVAC Unit / Water heater re-work |
| 2026/05/19 | Electrical | Ceiling Rough-in | Failed | Rocky Wilde | Bathroom / Locker room / soffits |
| 2026/05/14 | Mechanical | Re-Inspection | Passed | Paul Nitz | |
| 2026/05/14 | Mechanical | Duct Rough-in | Passed | Paul Nitz | |
| 2026/05/13 | Mechanical | Wall & Ceiling | Failed | Paul Nitz | Above ceiling Mechanical only including soffits. Not Ready 1) flex ducts are not connected 2) access openings are missing 3) soffit framing has not been inspected |
| 2026/04/24 | Electrical | Wall Rough-in | Passed | James Melvin | |
| 2026/04/22 | Electrical | Wall Rough-in | James Melvin | ||
| 2026/04/16 | Building/Structural | Sheetrock | Passed | Paul Nitz | Screw insp on sheetrock |
| 2026/04/13 | Electrical | Wall Rough-in | Passed | James Melvin | |
| 2026/04/09 | Other | Stormwater | Cancelled | Rocky Wilde | |
| 2026/04/06 | Building/Structural | Insulation | Passed | Paul Nitz | Partial insulation insp for top out board cover. |
| 2026/04/03 | Building/Structural | Roofing | Passed | Paul Nitz | in progress |
| 2026/04/02 | Plumbing | Rough-in | Passed | Paul Nitz | |
| 2026/04/02 | Plumbing | Stack Piping & Test | Passed | Paul Nitz | |
| 2026/04/02 | Plumbing | Water Piping & Test | Passed | Paul Nitz | |
| 2026/04/02 | Building/Structural | Framing | Passed | Paul Nitz | Frame insp for top out board in rooms 114,118,116,115,111,117,113, |
| 2026/03/31 | Building/Structural | Roofing | Passed | Kody Boswell | Clubhouse Roof Insulation insp for Metal roof installs. |
| 2026/03/31 | Building/Structural | Insulation | Passed | Kody Boswell | Clubhouse Roof Insulation insp for Metal roof installs. |
| 2026/03/27 | Building/Structural | Framing | Passed | Kody Boswell | This is for high sheetrock installs only. |
| 2026/03/26 | Building/Structural | Masonry | NOT READY | Kody Boswell | Mech Yard CMU wall Contractor had finished 2 of the 3 walls |
| 2026/03/25 | Building/Structural | Masonry | NOT READY | Kody Boswell | Mech yard wall top out for grout. FSU BCA showed up on site and the mason was still laying block. |
| 2026/03/24 | Plumbing | Underground | Passed | Rocky Wilde | |
| 2026/03/24 | Building/Structural | Sheetrock | Passed | Kody Boswell | Electrical room only screw inspection for tape and mud. |
| 2026/03/19 | Building/Structural | Framing | Passed | Kody Boswell | Electrical room / Wall top out discussion / approval. |
| 2026/03/19 | Plumbing | Underground | Passed | Paul Nitz | Storm water UG at Clubhouse |
| 2026/03/18 | Mechanical | Re-Inspection | Passed | Paul Nitz | |
| 2026/03/18 | Mechanical | Duct Pressure Test | Passed | Paul Nitz | |
| 2026/03/13 | Mechanical | Duct Rough-in | Failed | Paul Nitz | Clubhouse / Thank you 1) Straps missing in multiple locations |
| 2026/03/13 | Mechanical | Duct Pressure Test | Failed | Paul Nitz | Clubhouse / Thank you 1) pressure could not be maintained |
| 2026/03/12 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for the sidewalk between Clubhouse and Field. |
| 2026/03/06 | Building/Structural | Slab | Conditional | Paul Nitz | This is an exterior sidewalk between the Clubhouse and the field. 1) an engineered letter will be required for the expansion “diamond shaped” joints missing around the columns |
| 2026/02/20 | Building/Structural | Structural | Passed | Kody Boswell | Reviewed reinforcing steel for 3 tie columns: 1) Along grid 6, near grid B 2) Along grid 2, between grids A-B 3) Along grid 2, at grid A The deficiencies noted on prior inspections were corrected. |
| 2026/02/20 | Building/Structural | Re-Inspection | Passed | Kody Boswell | Reviewed reinforcing steel for 3 tie columns: 1) Along grid 6, near grid B 2) Along grid 2, between grids A-B 3) Along grid 2, at grid A The deficiencies noted on prior inspections were corrected. |
| 2026/02/18 | Building/Structural | Structural | Failed | Kody Boswell | Reviewed reinforcing steel for 3 tie columns: 1) Along grid 6, near grid B 2) Along grid 2, between grids A-B 3) Along grid 2, at grid A The following deficiencies must be corrected: 1) The plate embed should be rotated 90° so that studs are oriented as shown in detail 6/S-601. 2) Bond beam reinforcing and horizontal CMU joint reinforcing should terminate inside of TC, as shown in detail 9/S-601. Masons were in the process of topping out bond beam at time of inspection. 3) The 4 additional ties as called out in detail 3/S-601 were not installed at the top of TC, they need to be added. |
| 2026/02/16 | Building/Structural | Structural | Failed | Kody Boswell | TC-2 vertical column rebar Reinforcing steel still needs correction as noted in inspection done on 2/13/2026 |
| 2026/02/16 | Building/Structural | Masonry | Conditional | Kody Boswell | Reviewed reinforcing steel for top out of several masonry walls. Result is condtional pending photos from Contractor showing horizontal reinforcing for top coarse of bond beams has been installed. |
| 2026/02/13 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for the mechanical pad located in the mechanical yard. Reinforcing steel was in substantial compliance with the contract drawings. |
| 2026/02/10 | Building/Structural | Structural | Failed | Kody Boswell | Reviewed reinforcing steel for 3 tie columns: 1) Along grid 6, near grid B 2) Along grid 2, between grids A-B 3) Along grid 2, at grid A The following deficencies must be corrected: 1) Chairs should be installed to provide adequate cover during concrete placement. The plate embed should be rotated 90° so that studs are oriented as shown in detail 6/S-601. It was noted during TC inspection that the top of CMU wall doesn’t appear to match detail 6/S-601. Verify top of CMU wall condition with EOR. 2) Chairs should be installed to provide adequate cover during concrete placement. Bond beam reinforcing and horizontal CMU joint reinforcing should terminate inside of TC, as shown in detail 9/S-601. 3) Chairs should be installed to provide adequate cover during concrete placement. Bond beam reinforcing should either be continuous through or terminate inside TC with hooks. Verify with EOR. The 4 additional ties as shown in detail 3/S-601 were not installed at thje top of TC, they need to be added. |
| 2026/01/22 | Building/Structural | Masonry | Passed | Paul Nitz | Re-Inspection for masonry 1) This was for the back wall corrections that Kody had failed on 01/21/2026 only. |
| 2026/01/22 | Building/Structural | Re-Inspection | Passed | Paul Nitz | Re-Inspection for masonry |
| 2026/01/21 | Building/Structural | Masonry | Failed | Kody Boswell | Reviewed reinforcing steel for CMU walls. There are still missing reinforcing bars for 5 locations where roof rafters bear on CMU wall. This was discussed with the Contractor while on site. |
| 2026/01/16 | Building/Structural | Re-Inspection | NOT READY | Kody Boswell | Reinspection Clubhouse CMU for rebar. Mason was not on site and CMU was not able to be accessed for inspection |
| 2026/01/14 | Building/Structural | Masonry | Failed | Kody Boswell | Reviewed reinforcing steel for the first lift of CMU walls (high lift). The back wall along grid A was missing reinforcing steel called out in details 3/S601 and 10/S601. Missing reinforcing is the "2 vertical bars at 8in. in solid grout". Contractor to contact EOR and verify if missing bars need to be drilled and epoxied into slab or not. Also, cleanouts have excessive debris that must be removed prior to close up and grouting. Contractor to request inspection after items above have been addressed. |
| 2026/01/14 | Building/Structural | Masonry | NOT READY | Kody Boswell | Masonry Rebar Masons were still laying block when FSU BCA arrived on site. Contractor requested FSU BCA to return to the site in the PM. |
| 2026/01/13 | Plumbing | Storm Piping & Test | Passed | Paul Nitz | civil stormwater behind clubhouse |
| 2025/10/24 | Building/Structural | Footing | Passed | Kody Boswell | Reviewed reinforcing steel for several foundations |
| 2025/10/22 | Building/Structural | Footing | Passed | Kody Boswell | Reviewed reinforcing steel for some LAX Clubhouse foundations |
| Building/Structural | Masonry | Postponed | Kody Boswell | CMU rebar at Clubhouse Contractor postponed inspection to a later date in order to use high lift grouting over low lift grouting. | |
| Building/Structural | Footing | Postponed | Kody Boswell | LAX Clubhouse foundations Contractor contacted FSU BCA prior to site arrival to cancel/postpone inspection | |
| Building/Structural | Structural | Postponed | Kody Boswell | Tie Columns at Clubhouse Inspection postponed | |
| Building/Structural | Re-Inspection | Passed | Rocky Wilde | ||
| Mechanical | Duct Pressure Test | Paul Nitz | Clubhouse / Thank you | ||
| Mechanical | Duct Rough-in | Paul Nitz | Clubhouse / Thank you |

BCA Project #: 24-03683- Ringling Banyon Café Rupp Pavilion Reno Phase II
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2026/05/12 | Roofing | In progress | Passed | Rocky Wilde |

BCA Project #: 24-03681- Wildwood North Bathroom Improvements
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2026/06/26 | Mechanical | Final Mechanical | Paul Nitz | This inspection is for above ceiling on the 3rd so they can close up | |
| 2026/06/26 | Plumbing | Final Plumbing | Passed | Paul Nitz | This inspection is for above ceiling on the 3rd so they can close up |
| 2026/06/22 | Building/Structural | Sheetrock | Passed | Paul Nitz | 1st floor screw inspection |
| 2026/06/18 | Building/Structural | Re-Inspection | Passed | Paul Nitz | 1) re-inspection for above ceiling on the 4th floor |
| 2026/06/18 | Mechanical | Final Mechanical | Passed | Paul Nitz | 1) re-inspection for above ceiling on the 4th floor |
| 2026/06/18 | Mechanical | Re-Inspection | Passed | Paul Nitz | 1) re-inspection for above ceiling on the 4th floor |
| 2026/06/18 | Building/Structural | Final Building | Cancelled | Paul Nitz | 1) re-inspection for above ceiling on the 4th floor 1) I scheduled the wrong inspectio. Paul Nitz |
| 2026/06/17 | Building/Structural | Wall/Ceiling | Conditional | Paul Nitz | for the exhaust install on the 4th floor |
| 2026/06/17 | Mechanical | Duct Rough-in | Conditional | Paul Nitz | for the exhaust install on the 4th floor |
| 2026/06/16 | Mechanical | Equipment | Passed | Paul Nitz | exhaust fan install on the 5th floor |
| 2026/06/16 | Building/Structural | Wall/Ceiling | Passed | Paul Nitz | exhaust fan install on the 5th floor |
| 2026/06/12 | Building/Structural | Insulation | Passed | Paul Nitz | |
| 2026/06/12 | Plumbing | Re-Inspection | Passed | Paul Nitz | |
| 2026/06/11 | Building/Structural | Insulation | Passed | Paul Nitz | |
| 2026/06/11 | Plumbing | Rough-in | Passed | Paul Nitz | |
| 2026/06/11 | Building/Structural | Insulation | Passed | Paul Nitz | |
| 2026/06/11 | Plumbing | Re-Inspection | Passed | Paul Nitz | |
| 2026/06/10 | Building/Structural | Insulation | Failed | Paul Nitz | 1) two bathrooms were missing insulation |
| 2026/06/10 | Plumbing | Rough-in | Passed | Paul Nitz | |
| 2026/06/05 | Plumbing | Other | Passed | Paul Nitz | Shower Drains First Floor |
| 2026/06/02 | Plumbing | Rough-in | Passed | Rocky Wilde | |
| 2026/06/02 | Building/Structural | Framing | Passed | Rocky Wilde | |
| 2026/05/28 | Building/Structural | Insulation | Passed | Paul Nitz | 2nd floor insulation |
| 2026/05/27 | Plumbing | Rough-in | Partial | Paul Nitz | Plumbing wall rough in 2nd floor bathrooms Partially approved. Some bathrooms had piping not secured. Bathrooms where piping wasn't secured will be verified on next inspection. |
| 2026/05/27 | Building/Structural | Framing | Passed | Paul Nitz | Framing on 2nd floor Plumbing wall rough in 2nd floor |
| 2026/05/27 | Plumbing | Water Piping & Test | Failed | Paul Nitz | Bathroom shower pan water tests for all bathrooms on the 5th floor. Two showers failed due to visible water leakage from new shower drain fittings. Contractor to fix leaking shower drain fittings and request re-inspection. |
| 2026/05/22 | Building/Structural | Sheetrock | Passed | Kody Boswell | Screw inspection on 3rd floor |
| 2026/05/21 | Building/Structural | Insulation | Passed | Paul Nitz | Insulation - 3rd floor |
| 2026/05/21 | Building/Structural | Sheetrock | Passed | Paul Nitz | Framing on 3rd floor Plumbing wall rough in 3rd floor Drywall screw inspection on 4th floor Shower pans on 5th floor |
| 2026/05/21 | Building/Structural | Framing | Passed | Paul Nitz | Framing on 3rd floor Plumbing wall rough in 3rd floor Drywall screw inspection on 4th floor Shower pans on 5th floor |
| 2026/05/20 | Plumbing | Rough-in | Passed | Paul Nitz | Plumbing wall rough in 3rd floor |
| 2026/05/20 | Building/Structural | Sheetrock | Passed | Kody Boswell | Reviewed sheetrock attachment to LG framing for all bathrooms on the 5th floor |
| 2026/05/18 | Building/Structural | Insulation | Passed | Kody Boswell | Reviewed insulation installation for bathroom walls, entire 4th floor. One bathroom had one area missing insulation. Discussed with Contractor and received photos later in the day showing the missing insulation was installed. |
| 2026/05/14 | Building/Structural | Framing | Conditional | Paul Nitz | 5th floor insulation 4th floor ceiling framing/framing repairs 4th floor plumbing wall rough (shower valves/toilet supply 1) Additional strapping will be required for the water closet supply lines |
| 2026/05/14 | Building/Structural | Insulation | Passed | Paul Nitz | 5th floor insulation 4th floor ceiling framing/framing repairs 4th floor plumbing wall rough (shower valves/toilet supply |
| 2026/05/14 | Plumbing | Rough-in | Passed | Paul Nitz | 5th floor insulation 4th floor ceiling framing/framing repairs 4th floor plumbing wall rough (shower valves/toilet supply |
| 2026/05/12 | Building/Structural | Framing | Passed | Paul Nitz | 5th floor bathrooms |
| 2026/05/12 | Plumbing | Rough-in | Passed | Paul Nitz | 5th floor bathrooms |

BCA Project #: 24-03677- BSIR Post Project Revisions
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2025/07/21 | Electrical | Final Electrical | Postponed | Rocky Wilde | ASI 5 electrical revisions. Rooms 0119P and 0119N. |
| 2025/07/11 | Electrical | Final Electrical | Passed | Al Smythe | Paul and Rocky, This inspection will be in room 0116 that was part of the BSIR Lab permit for the 0119 suite. It's the one we discussed this past Tuesday morning. Thanks, Larry |
| 2025/07/11 | Plumbing | Final Plumbing | Passed | Paul Nitz | Paul inspected this on 7/11/25. Room 116 emergency shower and eyewash. |
| 2025/07/11 | Mechanical | Final Mechanical | Passed | Paul Nitz | Paul and Rocky, This inspection will be in room 0116 that was part of the BSIR Lab permit for the 0119 suite. It's the one we discussed this past Tuesday morning. Thanks, Larry |
| 2025/06/16 | Electrical | Final Electrical | Passed | Rocky Wilde | This final will be for 0119P and 0119Q in the BSIR Lab. It was agreed upon, that the whips in question will actually be a part of the equipment and will connect to the disconnects. Thank you, Larry |
| Electrical | Ceiling Rough-in | Passed | Rocky Wilde | This inspection will be in room 0119. Larry |

BCA Project #: 24-03674- Strozier Sub-Basement Upgrades
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2026/04/30 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for a portion of exterior slab on grade |
| 2026/04/21 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for exterior stairs on west end of building |
| 2026/04/08 | Building/Structural | Masonry | Passed | Kody Boswell | Reviewed reinforcing steel for exterior CMU walls locateda th the NW stair |
| 2026/03/31 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for 2 footings for new exterior CMU/brick walls and for new exterior stairs |
| 2026/03/19 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for exterior slab on grade |
| 2026/03/11 | Building/Structural | Erosion Control | Passed | Kody Boswell | Reviewed reinforcing steel for the north side curb along the exterior wall of the building |
| 2026/02/18 | Building/Structural | Footing | Passed | Kody Boswell | Reviewed reinforcing steel for planter box at the north east corner of the building |
| 2026/02/13 | Building/Structural | Structural | Passed | Paul Nitz | This is a steel inspection for the new walkway and steps on the east side fire escape we intend to pour Monday morning |
| 2026/02/13 | Building/Structural | Slab | Passed | Paul Nitz | This is a steel inspection for the new walkway and steps on the east side fire escape we intend to pour Monday morning |
| 2026/02/03 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for trench infills in several areas |
| 2026/01/21 | Building/Structural | Masonry | Passed | Kody Boswell | Reviewed reinforcing steel for CMU walls for the new stair exterior of the NE corner of the building |
| 2026/01/21 | Building/Structural | Structural | Passed | Kody Boswell | Reviewed reinforcing steel for CMU walls for the new stair exterior of the NE corner of the building |
| 2026/01/14 | Building/Structural | Footing | Conditional | Kody Boswell | Reviewed reinforcing steel for footers for new walls at sidewalk near the NE corner of the building. Contractor was in the process of placing wall dowels when FSU BCA arrived on site. Result is conditional pending photo(s) from the Contractor showing wall dowels have been installed. |
| 2026/01/14 | Fire Safety | Final Egress/Emergency Lights | Conditional | Curtis Rogers | Requesting a fire egress inspection to close down the East side emergency stair of Strozier Library |
| Building/Structural | Footing | Postponed | Kody Boswell | Contractor contacted FSU BCA prior to site arrival to postpone inspection to a later date. | |
| Building/Structural | Structural | Cancelled | Kody Boswell | Rebar for pour on Tuesday morning Contractor cancelled inspection via email | |
| Building/Structural | Structural | Cancelled | Kody Boswell | Rebar for pour on Tuesday morning Contractor cancelled inspection via email | |
| Building/Structural | Slab | Cancelled | Kody Boswell | This is for sidewalk aera on west end of building Contractor contacted FSU BCA prior to site arrival to cancel/postpone inspection |

BCA Project #: 24-03660-C Panama City Tech B South Multi Building
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2026/05/06 | Building/Structural | Roofing | Passed | Paul Nitz | |
| 2026/05/06 | Building/Structural | Final Building | Failed | Paul Nitz | 1) An engineered letter will be required for the window frame installation stating that it meets the installation instructions as well as the wind load, this inspection was not performed by FSU BCA 2) Weep holes that were improperly placed per manufacture installation need to be repaired and properly installed 3) Broken window needs to be replaced and inspected 4) Weep holes that were not installed in multiple locations need to be added 5) Broken door glass needs to be repaired and inspected 6) ADA door operator needs to be repaired or adjusted for proper working operation |
| 2026/05/06 | Electrical | Final Electrical | Passed | James Melvin |

BCA Project #: 24-03641- Ringling Art Museum Roof Replacement
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2026/06/10 | Building/Structural | Roof Final | Passed | Rocky Wilde | final roofing inspection |

BCA Project #: 24-03628-A Bio Unit 1 - Second Floor Remodling
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2026/06/08 | Building/Structural | Sheetrock | Passed | Kody Boswell | Drywall Screw Inspection |
| 2026/06/04 | Building/Structural | Framing | Passed | Rocky Wilde | New Wall at east main stairwell 2nd floor |
| 2026/06/04 | Electrical | Wall Rough-in | Passed | Rocky Wilde | New Wall at East Main Stairwell 2nd floor |
| 2026/05/29 | Mechanical | Duct Rough-in | Passed | Paul Nitz | Room 0241 for AHU 2-1 |
| 2026/05/27 | Mechanical | Wall & Ceiling | Passed | Paul Nitz | Rooms 2001,2001A,2001B,2001C,2007,2208,2009,2011,2012, 2013, 2013A, 2014, 2015, 2015A, 2016, 2017, 2018, 2019, 2020, 2021, 2022, 2023, 2025, 2025A, 2028, 2028A, 2029, 2030, 2031. Above Ceiling |
| 2026/05/22 | Fire Safety | Fire Water Above Ground | Partial | Curtis Rogers | ***Acoustic Ceilings ***Above Ceiling |
| 2026/05/22 | Fire Safety | Fire Alarm Rough-In | Passed | Curtis Rogers | Curtis Rogers inspected this on 5/22/2026 also. |
| 2026/05/22 | Fire Safety | Fire Water Above Ground | Partial | Curtis Rogers | Curtis Rogers inspected this on 5/22/2026 also. |
| 2026/05/21 | Mechanical | Wall & Ceiling | Failed | Paul Nitz | Rooms that are ready; 2000, 2001, 2001A, 2001C, 2007, 2007A, 2008, 2009, 2011, 2012, 2013, 2013A, 2014, 2015, 2015A, 2016, 2017, 2022, 2023, 2025, 2028, 2029, 2030, and 2031 1) Supply, return, and exhaust duct labeling missing 2) Saddles on plumbing missing 3) Insulation on grills missing 4) some ducting has not been installed 5) labeling missing on the plumbing lines 6) check access openings for the fire dampers 7) |
| 2026/05/21 | Electrical | Ceiling Rough-in | Passed | Rocky Wilde | Rooms that are ready; 2000, 2001, 2001A, 2001C, 2007, 2007A, 2008, 2009, 2011, 2012, 2013, 2013A, 2014, 2015, 2015A, 2016, 2017, 2022, 2023, 2025, 2028, 2029, 2030, and 2031 |
| 2026/05/18 | Building/Structural | Sheetrock | Passed | Paul Nitz | Partial wall in mechanical room 0241 |
| 2026/05/12 | Building/Structural | Sheetrock | Passed | Kody Boswell | Photos sent to Kody Boswell for inspection. Partial wall in 2015 lab screw inspection. |
| 2026/05/07 | Electrical | Wall Rough-in | Passed | Rocky Wilde | Electrical wall rough in for mechanical divider wall in room 2015. |
| 2026/05/07 | Building/Structural | Framing | Passed | Kody Boswell | Mechanical divider wall framing in room 2015. |
| 2026/05/04 | Mechanical | Insulation | Passed | Paul Nitz | Partial insulation inspection for ductwork in mechanical room 0242. Paul Nitz looked at this on 4-27-26 |
| 2026/05/01 | Mechanical | CHW Piping & Test | Passed | Paul Nitz | This is for CHW piping in mechanical rooms 0241 & 0242 to both AHU's. |
| 2026/04/14 | Electrical | Floor Rough-in | Passed | Rocky Wilde | Inspection will be in suite 119 on 1st floor for floor boxes in 2nd floor labs 2011 and 2012. |
| 2026/04/09 | Electrical | Floor Rough-in | Cancelled | Rocky Wilde | Inspection will be in 119 suite on 1st floor for floor boxes in 2nd floor labs 2011 and 2012. |
| 2026/03/27 | Building/Structural | Sheetrock | Passed | Rocky Wilde | Screw inspection for mechanical wall in prep room 2015A. Rocky Wilde passed inspection on 3-26-26. |
| 2026/03/26 | Electrical | Floor Rough-in | Passed | Rocky Wilde | This inspection will be in rooms 116 ,113, 104B, 104, 103, 101, and 101A. |
| 2026/03/19 | Building/Structural | Framing | Passed | Paul Nitz | The inspection will be in room 2015A. |
| 2026/03/19 | Electrical | Wall Rough-in | Passed | Rocky Wilde | The inspection will be in room 2015A. |
| 2026/03/16 | Building/Structural | Sheetrock | Passed | Kody Boswell | Reviewed sheathing attachment to LG framing in several areas |
| 2026/03/16 | Building/Structural | Framing | Passed | Kody Boswell | Reviewed LG framing for 2 soffits |
| 2026/03/10 | Electrical | Floor Rough-in | Passed | Rocky Wilde | This inspection will be rooms 116, 117, and 118. Thank you, Larry |
| 2026/03/09 | Plumbing | Rough-in | Passed | Paul Nitz | Framing in the elevator lobby and plumbing at the emergency showers. |
| 2026/03/09 | Building/Structural | Framing | Passed | Paul Nitz | Framing in the elevator lobby and plumbing at the emergency showers. |
| 2026/02/26 | Electrical | Floor Rough-in | Passed | Rocky Wilde | This inspection will be above the ceiling in room 100. Thank you, Larry |
| 2026/02/24 | Mechanical | Duct Rough-in | Passed | Paul Nitz | Partial VAV connections. |
| 2026/02/17 | Building/Structural | Sheetrock | Passed | Kody Boswell | Screw inspection for several areas |
| 2026/02/09 | Building/Structural | Insulation | Passed | Paul Nitz | HW piping inwall. |
| 2026/02/09 | Electrical | Wall Rough-in | Passed | Rocky Wilde | Restroom wall auto operator electrical rough ins. |
| 2026/02/05 | Electrical | Wall Rough-in | Passed | Rocky Wilde | 2013 dividing wall at storage 2010. |
| 2026/02/05 | Building/Structural | Insulation | Passed | Paul Nitz | |
| 2026/02/05 | Plumbing | Stack Piping & Test | Passed | Paul Nitz | Rooms 2023, 2025, and 2028 |
| 2026/02/04 | Plumbing | Stack Piping & Test | Passed | Rocky Wilde | 2013, 2013A, 2015, and 2015A. |
| 2026/02/03 | Plumbing | Water Piping & Test | Passed | Paul Nitz | DCW and HW in rooms 2013, 2015, and 2015A. DI water in rooms 2014, 2015, 2015A, 2013A, 2025A, and 2028A. |
| 2026/01/30 | Plumbing | Stack Piping & Test | Passed | Paul Nitz | Rooms 2013, 2015, 2015A, 2025A, 2028 and 2031. |
| 2026/01/29 | Fire Safety | Hydro-Test | Passed | Curtis Rogers | |
| 2026/01/28 | Mechanical | Duct Rough-in | Passed | Paul Nitz | |
| 2026/01/27 | Mechanical | Duct Pressure Test | Passed | Paul Nitz | |
| 2026/01/27 | Mechanical | Duct Pressure Test | Passed | Paul Nitz | |
| 2026/01/27 | Plumbing | Water Piping & Test | Passed | Paul Nitz | Partial DCW and HW return & supply. |
| 2026/01/27 | Plumbing | Stack Piping & Test | Passed | Paul Nitz | Rooms 2007, 2011, 2012, and 2014. |
| 2026/01/22 | Building/Structural | Sheetrock | Passed | Paul Nitz | Gang and HC baths |
| 2026/01/20 | Electrical | Wall Rough-in | Passed | Rocky Wilde | Partial elevator wall. |
| 2026/01/15 | Building/Structural | Framing | Passed | Kody Boswell | Reviewed LG framing for several walls |
| 2026/01/13 | Electrical | Wall Rough-in | Passed | Rocky Wilde | Inspections will be in the gang baths. |
| 2026/01/13 | Building/Structural | Framing | Passed | Paul Nitz | Inspections will be in the gang baths. |
| 2026/01/12 | Mechanical | Duct Rough-in | Passed | Paul Nitz | |
| 2026/01/12 | Mechanical | CHW Piping & Test | Passed | Paul Nitz | CHW piping to serve AHU 2.1 |
| 2026/01/08 | Building/Structural | Sheetrock | Passed | Kody Boswell | Reviewed sheathing attachment to LG framing in several areas |
| 2026/01/07 | Mechanical | HW Piping & Test | Passed | Paul Nitz | |
| 2025/12/30 | Electrical | Wall Rough-in | Passed | Rocky Wilde | If you don't have card access to the building, the exterior door is unlocked on the north end of the building at the service road. Thanks, Larry |
| 2025/12/22 | Mechanical | CHW Piping & Test | Passed | Rocky Wilde | This is hydro test/ inspection for Glycol piping. |
| 2025/12/22 | Building/Structural | Sheetrock | Passed | Rocky Wilde | |
| 2025/12/22 | Plumbing | Water Piping & Test | Passed | Rocky Wilde | Inspection for water piping in restrooms on 2nd floor. |
| 2025/12/18 | Building/Structural | Sheetrock | Passed | Paul Nitz | |
| 2025/12/18 | Building/Structural | Framing | Passed | Paul Nitz | |
| 2025/12/18 | Building/Structural | Insulation | Passed | Paul Nitz | |
| 2025/12/15 | Mechanical | Duct Pressure Test | Failed | Paul Nitz | This inspection will be with Vause Mechanical. 1) Duct pressure test failed, ducts would not hold the minimum pressure specified on the plans |
| 2025/12/12 | Mechanical | Re-Inspection | Passed | Paul Nitz | CHW piping to serve AHU-4 |
| 2025/12/12 | Mechanical | CHW Piping & Test | Passed | Paul Nitz | CHW piping to serve AHU-4 |
| 2025/12/10 | Mechanical | Duct Rough-in | Passed | Paul Nitz | Partial mechanical duct rough in. Paul looked at this on 12-10-25. |
| 2025/12/10 | Mechanical | CHW Piping & Test | Failed | Paul Nitz | Inspection for CHW piping to serve AHU 4. 1) air in the hydro test lines |
| 2025/12/10 | Mechanical | Duct Pressure Test | NOT READY | Paul Nitz | This inspection will be with Vause Mechanical. Larry |
| 2025/12/09 | Building/Structural | Sheetrock | Passed | Paul Nitz | These inspections will be in room 2001. 1) first layer on the fire wall |
| 2025/12/09 | Electrical | Wall Rough-in | Passed | Rocky Wilde | These inspections will be in room 2001. |
| 2025/12/08 | Electrical | Wall Rough-in | Passed | Rocky Wilde | This inspection will be for the following rooms, 2001A, 2001B, 2001C, 2008, 2009, 2017, 2018, 2019, 2020, 2021 and 2022. Thank you, |
| 2025/12/05 | Plumbing | Rough-in | Passed | Paul Nitz | This inspection will be in the 1st and 2nd floor gang baths. Larry |
| 2025/12/05 | Plumbing | Stack Piping & Test | Passed | Paul Nitz | This inspection will be in the 1st and 2nd floor gang baths. Larry |
| 2025/12/03 | Plumbing | Water Piping & Test | NOT READY | Paul Nitz | This inspection will be in the two gang bathrooms and the H/C bathroom. Larry |
| 2025/12/03 | Plumbing | Stack Piping & Test | NOT READY | Paul Nitz | This inspection will be in the two gang bathrooms and the H/C bathroom. Larry |
| 2025/12/03 | Plumbing | Rough-in | NOT READY | Paul Nitz | This inspection will be in the two gang bathrooms and the H/C bathroom. Larry |
| 2025/12/03 | Building/Structural | Sheetrock | Passed | Paul Nitz | Screw inspection in room 2007 |
| 2025/12/02 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for 2 slab infills in lab areas |
| 2025/12/01 | Electrical | Wall Rough-in | Passed | Rocky Wilde | This will be a partial in room 2027. The framing inspection passed on 11-25-2025. We'd like to complete this room in order to relocate the fire alarm equipment. Larry |
| 2025/11/25 | Building/Structural | Sheetrock | Passed | Kody Boswell | top out |
| 2025/11/25 | Building/Structural | Framing | Passed | Kody Boswell | |
| 2025/11/20 | Building/Structural | Masonry | Passed | Kody Boswell | Reviewed reinforcing steel for CMU sill for new window in office 2019 |
| 2025/11/19 | Building/Structural | Sheetrock | Partial | Paul Nitz | Please call when you get here and we'll get everyone gathered. Thanks, Larry |
| 2025/11/19 | Mechanical | Duct Rough-in | Partial | Paul Nitz | Please call when you get here and we'll get everyone gathered. Thanks, Larry |
| 2025/11/19 | Building/Structural | Masonry | Passed | Kody Boswell | Reviewed reinforcing steel for CMU jambs and header for new window in office 2019. |
| 2025/11/19 | Building/Structural | Structural | Passed | Kody Boswell | Reviewed reinforcing steel for CMU jambs and header for new window in office 2019. |
| 2025/11/19 | Building/Structural | Framing | Passed | Kody Boswell | Reviewed LG framing in rooms 2016,2017,2018,2019,2020,2021, and 2022. |
| 2025/11/17 | Building/Structural | Sheetrock | Partial | Paul Nitz | This will be a screw inspection for some of the top out areas. Larry |
| 2025/11/17 | Building/Structural | Framing | Partial | Paul Nitz | This inspection was completed on 1-17-2025. Thank you, Larry |
| 2025/11/06 | Building/Structural | Framing | Conditional | Paul Nitz | Paul, We are asking for a courtesy inspection regarding the gyp board top out areas located in the open corridors. We'd like to hang the open corridor side of the wall, finish and paint the walls, the exposed structural steel and deck above. Larry |

BCA Project #: 24-03628- Bio Unit One Second Floor Remodeling
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2026/02/13 | Electrical | Wall Rough-in | Passed | Rocky Wilde | Call before to discuss. |
| 2025/11/17 | Building/Structural | Framing | Partial | Paul Nitz | This inspection was completed on 11-17-2025. Thank you, Larry |
| 2025/11/06 | Building/Structural | Framing | Conditional | Paul Nitz | Thanks for the help today, Larry |

BCA Project #: 24-03625- Sliger Data Center Chiller
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2025/07/02 | Mechanical | CHW Piping & Test | Passed | Paul Nitz |

BCA Project #: 24-03623- Westcott Ruby Diamond OVPR Suite Modifications
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2025/09/03 | Building/Structural | Final Building | Passed | Kody Boswell | Final building inspection. Project can be closed out. |
| 2025/08/22 | Plumbing | Final Plumbing | Passed | Paul Nitz | |
| 2025/07/15 | Electrical | Final Electrical | Failed | Rocky Wilde | open boxes, several boxes need to be labeled |
| 2025/07/11 | Plumbing | Final Plumbing | Failed | Paul Nitz | 1) Plans call for a brass p trap 2) Plans call for a angle valve 3) Water supply line needs supported |
| 2025/07/11 | Mechanical | Insulation | Passed | Paul Nitz | |
| 2025/06/30 | Mechanical | Duct Rough-in | Passed | Paul Nitz | |
| 2025/06/30 | Building/Structural | Wall/Ceiling | Passed | Paul Nitz | Cieling grid inspection |
| 2025/06/09 | Building/Structural | Sheetrock | Passed | Kody Boswell | Reviewed sheathing attachment for one new partiiton wall and two door infill areas |
| 2025/06/05 | Electrical | Wall Rough-in | Passed | James Melvin | |
| 2025/05/30 | Building/Structural | Framing | Conditional | Kody Boswell | Reviewed LG framing for a new partition wall and two door infills. Result is conditional pending addional bracing installation at the top of new partition wall. |
| 2025/05/21 | Plumbing | Rough-in | Passed | Paul Nitz |

BCA Project #: 24-03619- Fine Arts Waterproofing
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2025/08/13 | Building/Structural | Framing | Passed | Paul Nitz | Inspection on new stairs 1) Gaps in stair wall over 4” wide need to be filled before final CC 2) Feet of stair landing support need to be grouted with non-shrinking grout before final CC |
| 2025/06/26 | Building/Structural | Slab | Passed | Kody Boswell | Inspection on sidewalk |
| 2025/06/20 | Building/Structural | Slab | Passed | Kody Boswell | Inspection on Wire for new concrete slab and sidewalk |
| 2025/06/17 | Building/Structural | Structural | Passed | Kody Boswell | Reviewed reinforcing steel for two site walls. |
| 2025/06/11 | Building/Structural | Footing | Passed | Kody Boswell | Reviewed reinforcing steel for new footers for walls around Radius classroom area |
| 2025/06/06 | Building/Structural | Slab | Passed | Kody Boswell | Inspection on Rebar for Pad at Fire egress area in front and steps on West side |
| 2025/05/30 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for sidewalk on the west side of the job site |
| 2025/05/27 | Building/Structural | Framing | Failed | Paul Nitz | Inspection on added Storm water box re-bar 1) an engineered letter will be required for the construction of the storm water box, FSU BCA has not received the plans for its construction 2) an engineered letter will be required for the deviation of the plans on how the 6" and 8" pipe were ran to the storm box. |
| 2025/05/27 | Building/Structural | Erosion Control | Passed | Paul Nitz | Inspection on remaining revisions storm water piping 1) this is for the 12" pipe inspectipon only |
| 2025/05/23 | Building/Structural | Erosion Control | Conditional | Paul Nitz | Inspection on revised itein 1) engineered plans required for the storm box tie in |
| 2025/05/06 | Building/Structural | Wall/Ceiling | Passed | Paul Nitz | Inspection on Final section of new Waterproofing |
| 2025/05/06 | Plumbing | Underground | Conditional | Paul Nitz | Inspection on final section of new Trench drain piping 1) not a final drainpipe inspection, there is still an incomplete section at the entrance of the buildings south side |
| 2025/04/29 | Plumbing | Underground | Passed | Paul Nitz | |
| 2025/04/29 | Building/Structural | Wall/Ceiling | Passed | Paul Nitz | Inspection on new Waterproofing system |
| 2025/04/25 | Building/Structural | Structural | Passed | Kody Boswell | In-progress inspection of new Waterproofing system, base bid scope of work. Contractor had one area where underlayment and drainage mat was installed and another area where underlayment installation was in progress. |

BCA Project #: 24-03615-A Dittmer Building Reroof
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2025/11/19 | Building/Structural | Roofing | Passed | Kody Boswell | In-Progress Inspection of PVC capsheet installation |

BCA Project #: 24-03615- Dittmer Building Envelope Parapet
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2025/10/09 | Building/Structural | Roofing | Passed | Paul Nitz | In-Progress Inspection - LWIC/Weld Plates |
| 2025/09/10 | Building/Structural | Re-Inspection | Passed | Kody Boswell | Reviewed LG framing for new roof parapet. The items specified for prior framing inspection were addressed. |
| 2025/09/10 | Building/Structural | Framing | Passed | Kody Boswell | Reviewed LG framing for new roof parapet. The items specified for prior framing inspection were addressed. |
| 2025/09/08 | Building/Structural | Structural | Passed | Kody Boswell | Reviewed steel framing for the new roof parapet |
| 2025/09/08 | Building/Structural | Framing | Conditional | Kody Boswell | Reviewed LG framing for the roof parapet. The following was observed: 1) There were a few LG connection screws and a few LG to structural steel connection PAFs. Fasteners were installed as BCA pointed them out. 2) There were a few vertical studs where the connection at the bottom track occurred at the prepunched location. Contractor was in the process of stiffening these locations when BCA left the site. Resolved with inspection on 9/10/2025 Inspection result is conditional pending item (2) above being completed. BCA will revisit the site this afternoon to confirm. |
| 2025/07/29 | Building/Structural | Roofing | Passed | Kody Boswell | Tear Off/Dry-In Inspection |
| Building/Structural | Structural | Postponed | Kody Boswell | Follow up from 9/8 inspection Contractor contacted FSU BCA prior to site arrival to postpone inspection | |
| Building/Structural | Framing | Postponed | Kody Boswell | Follow up from 9/8 inspection Contractor contacted FSU BCA prior to site arrival to postpone inspection |

BCA Project #: 24-03607- UCB 4th and 5th Floor Modifications
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2025/04/18 | Mechanical | Final Mechanical | Passed | Rocky Wilde | All missing electrical covers have been installed and T&B sent |
| 2025/04/18 | Building/Structural | Final Building | Failed | Rocky Wilde | All missing electrical covers have been installed and T&B sent 1) signage missing |
| 2025/04/18 | Electrical | Final Electrical | Passed | Rocky Wilde | All missing electrical covers have been installed and T&B sent |
| 2025/04/14 | Electrical | Final Electrical | Failed | Paul Nitz | 1) outlet covers are still missing, this is the third failure for final electrical for this project |
| 2025/04/14 | Mechanical | Final Mechanical | Conditional | Paul Nitz | 1) Test And Balance report required |
| 2025/04/14 | Fire Safety | Final Fire Safety | Passed | Mary Creason | |
| 2025/03/28 | Fire Safety | Final Fire Safety | NOT READY | Mary Creason | Contractor not ready for a final - no door hardware, no glass panels on doors to hallways, electrical sockets not covered, tape on fire alarm devices due to painting, etc. |
| 2025/03/28 | Fire Safety | Final Fire Sprinkler | Passed | Mary Creason | |
| 2025/03/28 | Mechanical | Final Mechanical | Conditional | Paul Nitz | TAB required |
| 2025/03/28 | Electrical | Final Electrical | Failed | Rocky Wilde | |
| 2025/03/26 | Building/Structural | Final Building | Failed | Paul Nitz | This inspection is for the fourth floor only. Please call 850.252.7910 20-30 minutes before you 1) missing final mechanical, electrical 2) missing windows, carpet, door handles, outlet covers |
| 2025/03/25 | Building/Structural | Final Building | Failed | Paul Nitz | This inspection is for the fourth floor only. Please call 850.252.7910 20-30 minutes before you 1) glass for offices are missing 2) door knobs are missing 3) carpet is missing 4) outlet covers are missing I called the contractor but have not received a call back |
| 2025/02/11 | Fire Safety | Final Fire Sprinkler | Passed | Sam Sevor | Please call 30 minutes ahead of time so I will make sure to be there for the walk thru. |
| 2025/02/10 | Electrical | Wall Rough-in | Passed | James Melvin | Please call 30 minutes ahead of time so I will make sure to be there for the walk thru. |
| 2025/02/10 | Mechanical | Duct Rough-in | Failed | Paul Nitz | Please call 30 minutes ahead of time so I will make sure to be there for the walk thru. 1) ducts need to be sealed |
| 2025/02/10 | Electrical | Ceiling Rough-in | Passed | James Melvin | Please call 30 minutes ahead of time so I will make sure to be there for the walk thru. |
| 2025/02/10 | Building/Structural | Sheetrock | Passed | Paul Nitz | Please call 30 minutes ahead of time so I will make sure to be there for the walk thru. |
| 2025/02/10 | Building/Structural | Wall/Ceiling | Passed | Paul Nitz | Please call 30 minutes ahead of time so I will make sure to be there for the walk thru. |
| 2025/01/13 | Electrical | Final Electrical | Passed | James Melvin | This inspection is for the 5th floor kitchen area. Super onsite is Charles Burges, his number is 8506934872. |
| 2025/01/13 | Building/Structural | Final Building | Conditional | Paul Nitz | This inspection is for the 5th floor kitchen area. Super onsite is Charles Burges, his number is 8506934872. 1) 5th floor is ok for CC, the fourth floor was not ready |
| 2025/01/13 | Fire Safety | Final Fire Safety | Passed | Sam Sevor | This inspection is for the 5th floor kitchen area. Super onsite is Charles Burges, his number is 8506934872. |
| 2025/01/06 | Electrical | Ceiling Rough-in | Passed | James Melvin | Call me 30 minutes in advance please. |
| 2025/01/03 | Mechanical | Duct Rough-in | Passed | Paul Nitz | Call me 30 minutes in advance please. |
| 2025/01/03 | Mechanical | Insulation | Passed | Paul Nitz | Call me 30 minutes in advance please. |
| 2025/01/03 | Mechanical | Final Mechanical | Passed | Paul Nitz | Call me 30 minutes in advance please. |
| 2025/01/03 | Fire Safety | Fire Water Above Ground | Passed | Curtis Rogers | Moved three heads. Pre Inspected by Kurt on 1/3/2025 and passed. |
| Electrical | Final Electrical | James Melvin | Call me 30 minutes in advance please. |

BCA Project #: 23-03567- FAMU-FSU Engineering Building A Building Envelope Improvements
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2026/05/21 | Building/Structural | Final Building | Passed | Paul Nitz | |
| 2026/05/01 | Building/Structural | Roofing | Passed | Kody Boswell | North Side roof coping flashing and North Main Entrance Lower roof flashing Inspection done virtually via photos provided by the Contractor |
| 2025/12/16 | Building/Structural | Wall/Ceiling | Passed | Kody Boswell | College of Engineering - West Entrance Curtain Glass Wall Replacement Removal of top coping flashing and replacing the old existing lower flashing with the new flashing. |
| 2025/08/07 | Building/Structural | Wall/Ceiling | Cancelled | Kody Boswell | South Connector Entrance Roof cap This turned into an on-site meeting discussing existing conditions that were encountered during the roof cap removal. The AOR was on site for this discussion. No inspection was performed due to unforseen conditions. |
| 2025/07/14 | Building/Structural | Wall/Ceiling | Passed | Kody Boswell | South Entrance Curtain Glass Wall panel replacements. |

BCA Project #: 23-03563- Sandels Building Envelope Repair
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2026/05/26 | Building/Structural | Framing | Passed | Paul Nitz | this inspection was for the rain leader in the mens bathroom. |
| 2026/05/26 | Plumbing | Final Plumbing | Passed | Paul Nitz | this inspection was for the rain leader in the mens bathroom. |
| 2026/05/26 | Plumbing | Rough-in | Passed | Paul Nitz | this inspection was for the rain leader in the mens bathroom. |
| 2026/05/26 | Building/Structural | Sheetrock | Passed | Paul Nitz | this inspection was for the rain leader in the mens bathroom. |
| 2026/05/22 | Plumbing | Re-Inspection | Passed | Paul Nitz | Sandels 2nd Flr Mens Restroom Storm Drain Piping Support Inspection |
| 2026/05/13 | Plumbing | Rough-in | Conditional | Paul Nitz | 1) Rain leader support in the mechanical room that is attached to the sound batt ceiling need to be verified by an engineer or architect that it will be able to support the weight. 2) Rain leader support that is attached to the hanging block of wood needs to be secured to a structural member. |
| 2026/05/12 | Electrical | Ceiling Rough-in | Passed | Rocky Wilde | Framing inspection for new soffit in men’s 2nd floor bathroom |
| 2026/05/12 | Building/Structural | Framing | Failed | Paul Nitz | Framing inspection for new soffit in men’s 2nd floor bathroom 1) Additional strapping will be required for the water closet supply lines |
| 2026/05/06 | Plumbing | Storm Piping & Test | Passed | Rocky Wilde | Smoke test on new roof drain piping. S&S letter in file |
| 2026/04/16 | Plumbing | Underground | Passed | Paul Nitz | Follow-up Inspection for Storm Drain |
| 2026/04/15 | Plumbing | Underground | Partial | Paul Nitz | Underground roof drain repair |
| 2026/01/30 | Building/Structural | Final Building | Passed | Kody Boswell | Partial final for scope of work in ASI #7 |
| 2025/12/19 | Building/Structural | Final Building | Passed | Rocky Wilde | final partial, 100 suite. Rooms in 100 suite are cleared to occupy. |
| Building/Structural | Other | Cancelled | Kody Boswell |

BCA Project #: 23-03539- NCF Pritzker Marine Building Exterior Improvements
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2025/09/22 | Electrical | Final Electrical | Passed | Rocky Wilde | |
| 2025/09/09 | Electrical | Final Electrical | Passed | Rocky Wilde | |
| 2025/06/27 | Roofing | In progress | Conditional | Hank Fulmer | dry in for the sloped sections of the roof were inspected. Installation of the peal and stick was installed per manufactures specifications. The original drip edge and flashing is remaining . This is a partial approval. |
| 2025/06/06 | Roofing | In progress | Conditional | Joan Lima | PARTIAL DRYIN IN PROGRESS SOUTH SIDE |
| 2025/04/22 | Electrical | Final Electrical | Passed | Hank Fulmer | |
| 2025/04/22 | Plumbing | Final Plumbing | Passed | Hank Fulmer | |
| 2024/11/18 | Electrical | Wall Rough-in | Passed | Hank Fulmer | |
| 2024/11/18 | Plumbing | Rough-in | Conditional | Steve Bell | |
| 2024/11/18 | Electrical | Wall Rough-in | Conditional | Steve Bell | |
| 2024/11/18 | Plumbing | Rough-in | Passed | Hank Fulmer | |
| 2024/11/05 | Building/Structural | Structural | Passed | Joseph Agriesti | |
| 2024/10/30 | Building/Structural | Slab | Passed | Steve Bell | |
| 2024/10/28 | Building/Structural | Slab | Failed | Steve Bell | FBC2023 SECTION 107 SUBMITTAL DOCUMENTS No construction documents on site. Please provide approved plans. 1 hr inspection time |
| 2024/10/25 | Electrical | Floor Rough-in | Failed | Steve Bell | |
| 2024/10/25 | Electrical | Wall Rough-in | Failed | Nicholas Ninos | PVC conduit was installed above dirt on plastic sheeting. Installation method is NEC compliant. No discrepancies noted. |
| 2024/10/25 | Building/Structural | Slab | Failed | Steve Bell | |
| 2024/10/25 | Building/Structural | Slab | Passed | Nicholas Ninos | |
| 2024/10/25 | Electrical | Floor Rough-in | Passed | Nicholas Ninos | |
| 2024/10/16 | Building/Structural | Structural | Passed | Hank Fulmer | Partial inspection passed. This is for te south wall, north stairs, and first two column walls. All steel was properly sized and palced. The depths and widths were correctly sized per plans. |
| 2024/09/20 | Building/Structural | Structural | Passed | Joseph Agriesti | |
| 2024/09/06 | Building/Structural | Footing | Passed | Joseph Agriesti | |
| 2024/08/29 | Building/Structural | Structural | Passed | Hank Fulmer | |
| 2024/08/21 | Plumbing | Gas Piping & Test | Passed | Joseph Agriesti | |
| 2024/08/21 | Building/Structural | Structural | Passed | Hank Fulmer | |
| 2024/08/19 | Plumbing | Gas Piping & Test | Passed | Joseph Agriesti | |
| 2024/08/09 | Building/Structural | Footing | Passed | Hank Fulmer |

BCA Project #: 23-03508-A Tucker Center Chiller Replacement
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2025/01/31 | Electrical | Appliance/Equipment | Passed | Rocky Wilde | No visit required. This was already looked at by Rocky Wilde this morning at 10am |
| 2025/01/31 | Electrical | Panel/Feeder | Passed | Rocky Wilde | No visit required. This was already looked at by Rocky Wilde this morning at 10am |
| 2025/01/30 | Mechanical | Cond. Piping & Test | Passed | Paul Nitz | Please call me when on the way |
| 2025/01/30 | Mechanical | CHW Piping & Test | Passed | Paul Nitz | Please call me when on the way |
| Electrical | Final Electrical | Postponed | James Melvin | Please complete final inspection for permit closeout. | |
| Mechanical | Final Mechanical | Postponed | James Melvin | Please complete final inspection for permit closeout. | |
| Mechanical | Final Mechanical | Paul Nitz | final boiler inspection | ||
| Plumbing | Final Plumbing | Paul Nitz | final boiler inspection |

BCA Project #: 23-03455-A Doak Campbell - East Stands Improvements Phase II
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2026/05/19 | Fire Safety | Final Fire Safety | Passed | Curtis Rogers | Elevator at gate J and heat trace |
| 2026/03/24 | Fire Safety | Re-Inspection | Conditional | Curtis Rogers | Heat trace ****Submit Heat Trace Specs • Need to test FA Relays with Siemens in conjunction with Heat Trace Panels • Double Check Submittals (In Ref to Heat Trace) |
| 2026/03/24 | Electrical | Appliance/Equipment | Passed | Rocky Wilde | Elevator mini split |
| 2026/03/12 | Fire Safety | Final Fire Sprinkler | Postponed | Curtis Rogers | Heat trace wire ****PLEASE RESCHEDULE*** |
| 2026/02/27 | Fire Safety | Final Fire Alarm | Passed | Curtis Rogers | Elevator at gate E (C-6). Tested Elevator Recall with Elevator Inspector. |
| 2026/02/27 | Fire Safety | Final Fire Alarm | Passed | Curtis Rogers | Elevator at gate E ( C-6 ) |
| 2025/12/18 | Fire Safety | Final Fire Alarm | Passed | Curtis Rogers | Scorebaord override |
| 2025/09/04 | Plumbing | Final Plumbing | Conditional | Paul Nitz | 1) ADA stall doors need to be self closing 2) sink carrier needs to be installed in mens ADA bathroom as per plans 3) door handle needs to be replaced as per plans 4) doors in mens bathroom need to be painted as per plans |
| 2025/08/29 | Fire Safety | Final Fire Safety | Passed | Curtis Rogers | Elevator Recall A6 & C5 -PASSED American Signal Test - PASSED Emergency Back Up Power Test on 08.22.25 PASSED Sprinkler Tested on 08.27.25 PASSED Final Fire Alarm Test PASSED *GLOBAL Fire Panel has (4) troubles on Panel (2) Troubles from UCA building (existing troubles) *Scoreboard Trouble Monitor - Waitng for Scoreboard Card to be installed *Existing Troubles on Fire Alarm panel will not affect the Fire Alarm from activating properly |
| 2025/08/29 | Fire Safety | Re-Inspection | Passed | Curtis Rogers | Elevator Recall A#6 Passed |
| 2025/08/28 | Building/Structural | Final Building | Passed | Kody Boswell | Final building inspection for temporary CO |
| 2025/08/28 | Fire Safety | Final Fire Alarm | Partial | Curtis Rogers | Elevator Recall Elevator C#5 PASSED ELEVATOR A#6 NOT READY Elevator A#7 *Out of Scope… Upgrade & Testing Next Year |
| 2025/08/28 | Fire Safety | Final Fire Safety | Partial | Curtis Rogers | Project: 23-03455-A-Doak Campbell - East Stands Improvements Phase II Date: 8/28/2025 By: Curtis Rogers Type: Fire Safety-Final Fire Alarm Results: Partial Notes: Elevator Recall Elevator C#5 PASSED ELEVATOR A#6 NOT READY Elevator A#7 *Out of Scope… Upgrade & Testing Next Year |
| 2025/08/28 | Plumbing | Re-Inspection | Conditional | Paul Nitz | Toilet in room 3212 was loose 1) ADA door in men’s bathroom is in the wrong location as per plans and FBC A604.8.1 2) Door handle in men’s room is not per plans 3) Door closer in men’s room has not been changed as per plans 4) ADA doors in women’s restroom do nor shut properly (self close) 5) Women’s restroom is missing placards on two of the doors |
| 2025/08/28 | Electrical | Final Electrical | Passed | Rocky Wilde | |
| 2025/08/27 | Plumbing | Re-Inspection | Conditional | Paul Nitz | The jobsite superintendent as well as the plumbing contractor assured BCA that the temporary fix for the toilet height will be addressed the week of 9/1/2025 and will be completed by 9/12/2025 before the second home game. The new ADA toilet in the men’s restroom will be fixed and inspected by BCA before 8/29/2025. The cleanout covers that are missing will not be a problem for temporary CO. If you have any questions, please let me know. 1) ADA toilet is set to high MAX height is 19” FBC A604.4 (The Plumbing Contractor Made A Temporary Fix to this problem because of parts not being available before 8/29/2025) and was approved by the building official to be in compliance. 2) Clean-out covers are missing 3) Toilet in men’s new ADA bathroom is not secure and the supply to it is not plumb 4) The drain for the sink in the new men’s bathroom is PVC and needs to be changed out to chrome. |
| 2025/08/27 | Electrical | Final Electrical | Passed | Rocky Wilde | |
| 2025/08/27 | Plumbing | Final Plumbing | Conditional | Paul Nitz | The jobsite superintendent as well as the plumbing contractor assured BCA that the temporary fix for the toilet height will be addressed the week of 9/1/2025 and will be completed by 9/12/2025 before the second home game. The new ADA toilet in the men’s restroom will be fixed and inspected by BCA before 8/29/2025. The cleanout covers that are missing will not be a problem for temporary CO. If you have any questions, please let me know. 1) ADA toilet is set to high MAX height is 19” FBC A604.4 (The Plumbing Contractor Made A Temporary Fix to this problem because of parts not being available before 8/29/2025) and was approved by the building official to be in compliance. 2) Clean-out covers are missing 3) Toilet in men’s new ADA bathroom is not secure and the supply to it is not plumb 4) The drain for the sink in the new men’s bathroom is PVC and needs to be changed out to chrome. |
| 2025/08/26 | Electrical | Final Electrical | Partial | Rocky Wilde | label electrical covers |
| 2025/08/26 | Building/Structural | Final Building | Failed | Rocky Wilde | 1) labeling missing 2) ADA doors must be self-closing. FBC A604.8.1.2 |
| 2025/08/26 | Fire Safety | Final Fire Sprinkler | Conditional | Curtis Rogers | *Need Riser Room Signage on each Riser Room *Add Inspector Test Pipe and Signs at the end of each Dry Sysytem *Add Extra Hanger Bracing for Dry System Riser Upper Concourse Level |
| 2025/08/26 | Mechanical | Final Mechanical | Passed | Paul Nitz | |
| 2025/08/26 | Fire Safety | Final Fire Safety | NOT READY | Curtis Rogers | |
| 2025/08/26 | Plumbing | Final Plumbing | Failed | Paul Nitz | 1) Trap primers are missing in the drains as per plans 2) ADA toilet is set to high MAX height is 19” FBC A604.4 3) Drinking fountain arch needs to be min 4” FBC A602.6 4) Clean-out covers are missing 5) Bathroom stalls need a minimum 15” clearance from partition/ obstacles FBC P405.3.1 6) Toilet in men’s new ADA bathroom is not secure and the supply to it is not plumb 7) The sink in the men’s new ADA bathroom is not hooked up |
| 2025/08/26 | Fire Safety | Final Fire Alarm | NOT READY | Curtis Rogers | *Need Elevator Up and Running to Complete Fire Alarm Inspections |
| 2025/08/26 | Fire Safety | Fire Water Above Ground | Passed | Curtis Rogers | Re inspection - Dry System #1 & 2 Upper Concourse Level East Stands *Trip Test - PASSED *Testing Fire Aalrm Components - PASSED |
| 2025/08/22 | Fire Safety | Final Fire Sprinkler | Failed | Curtis Rogers | Passed*Dry System on Phase 1 LLC East FAILED***(2) Dry Sytems on Phase 2 Upper Concourse Levels- Both Clappers(diapragms) not holding pressure |
| 2025/08/22 | Fire Safety | Final Egress/Emergency Lights | Passed | Curtis Rogers | We are scheduled to shut power down at 6 am to confirm generator switch over Passed *Back Up Power |
| 2025/08/22 | Fire Safety | Fire Water Above Ground | Passed | Curtis Rogers | Visual AboveGround Sprinkler |
| 2025/08/19 | Fire Safety | Hydro-Test | Passed | Curtis Rogers | PASSED*Hydro-Tested 2 Dry Systems East Stands Upper Concourse Level PASSED* Above Ceiling Inpsection |
| 2025/08/14 | Electrical | Panel/Feeder | Passed | Rocky Wilde | |
| 2025/08/11 | Building/Structural | Slab | Conditional | Kody Boswell | Reviewed structural steel, stel deck, and reinforcing steel for the elevated slab infill located on the 4th floor, section 15. Result is conditional pending installation of steel bracing. Contractor is allowed to place concrete prior to brace installation per the EOR. |
| 2025/08/11 | Building/Structural | Structural | Conditional | Kody Boswell | Reviewed structural steel, stel deck, and reinforcing steel for the elevated slab infill located on the 4th floor, section 15. Result is conditional pending installation of steel bracing. Contractor is allowed to place concrete prior to brace installation per the EOR. |
| 2025/08/01 | Building/Structural | Structural | Conditional | Kody Boswell | Re inspection for new slab at section 5- 4th floor Reviewed structural steel framing, steel decking, and elevated slab reinforcing for the slab infill area on the upper concourse in section 5. The following deficiences, originally reported on 7/30/2025, were corrected or in the process of being corrected while on site: - Steel framing along grid G didn't match what was shown in detail 1/S615. The W14x22 beam was placed offset from the existing column and some bracing was missing. - Steel framing along grid G didn't match what was shown in detail 2/S615. The W18x48 columns weren't installed. - Wire mesh slab reinforcing was sitting directly on steel deck. Wire mesh should be chaired over beams. Result is conditional pending receipt of photos from Contractor verifying items discussed on site were completed. |
| 2025/08/01 | Building/Structural | Slab | Conditional | Kody Boswell | Re inspection for new slab at section 5- 4th floor Reviewed structural steel framing, steel decking, and elevated slab reinforcing for the slab infill area on the upper concourse in section 5. The following deficiences, originally reported on 7/30/2025, were corrected or in the process of being corrected while on site: - Steel framing along grid G didn't match what was shown in detail 1/S615. The W14x22 beam was placed offset from the existing column and some bracing was missing. - Steel framing along grid G didn't match what was shown in detail 2/S615. The W18x48 columns weren't installed. - Wire mesh slab reinforcing was sitting directly on steel deck. Wire mesh should be chaired over beams. Result is conditional pending receipt of photos from Contractor verifying items discussed on site were completed. |
| 2025/07/31 | Fire Safety | Fire Alarm Rough-In | Conditional | Curtis Rogers | Fire alarm device test for the east side *Notification devices (Speaker Strobes) *Gate M - Outside Pump Room- Lower Speaker Strobe to the correct height - 84 inches to center *Gate E - Mens Restroom- Install Speaker Strobes Inside and Outside for proper coverage |
| 2025/07/31 | Plumbing | Water Piping & Test | Passed | Rocky Wilde | Water supply under new bathrooms on 4th floor section 7 and 13 |
| 2025/07/30 | Building/Structural | Slab | Failed | Kody Boswell | Reviewed structural steel framing, steel decking, and elevated slab reinforcing for the slab infill area on the upper concourse in section 5. The following deficiences were observed: - Steel framing along grid G didn't match what was shown in detail 1/S615. The W14x22 beam was placed offset from the existing column and some bracing was missing. - Steel framing along grid G didn't match what was shown in detail 2/S615. The W18x48 columns weren't installed. - Wire mesh slab reinforcing was sitting directly on steel deck. Wire mesh should be chaired over beams. |
| 2025/07/02 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel and and new steel deck attachment to existing structural steel framing for slab repair on ramp at column line 6n-7n vertical line K-L . North side of gate K |
| 2025/07/02 | Building/Structural | Structural | Passed | Kody Boswell | Reviewed reinforcing steel and and new steel deck attachment to existing structural steel framing for slab repair on ramp at column line 6n-7n vertical line K-L . North side of gate K |
| 2025/06/30 | Building/Structural | Sheetrock | Passed | Paul Nitz | Screw inspection new 4th floor bathrooms section 7 and 13 |
| 2025/06/27 | Building/Structural | Insulation | Passed | Kody Boswell | New bathrooms 4th floor section 7 and 13 ceiling insulation, upper concourse |
| 2025/06/27 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for mid level gate K ramp replacement |
| 2025/06/27 | Building/Structural | Structural | Passed | Kody Boswell | Reviewed steel framing and steel deck attachmnet for mid level gate K ramp |
| 2025/06/26 | Building/Structural | Masonry | Passed | Paul Nitz | Final lift steel prior to grout 4th floor section 7 and 13. Passing Verified by Paul |
| 2025/06/26 | Building/Structural | Structural | Postponed | Kody Boswell | Mid Level ramp repairs gate K Contractor contacted FSU BCA prior to site arrival to postpone inspection to a later date. |
| 2025/06/26 | Building/Structural | Slab | Postponed | Kody Boswell | Mid Level ramp repairs gate K Contractor contacted FSU BCA prior to site arrival to postpone inspection to a later date. |
| 2025/06/25 | Building/Structural | Masonry | Failed | Paul Nitz | Final lift rebar prior to grout 4th floor section 7 and 13 1) vertical bars not in contact with the grade beam |
| 2025/06/24 | Electrical | Ceiling Rough-in | Passed | Rocky Wilde | New 4th floor bathrooms |
| 2025/06/24 | Building/Structural | Masonry | Passed | Kody Boswell | Reviewed reinforcing steel for 1st lift of CMU walls for new fire suppression rooms attached to new bathrooms 4th floor section 7 and 13 |
| 2025/06/13 | Building/Structural | Slab | Passed | Rocky Wilde | Re-Inspection for 4th floor slab repair column line 2north- 1 east at top of k gate ramp |
| 2025/06/13 | Building/Structural | Structural | Passed | Rocky Wilde | Re-Inspection for 4th floor slab repair column line 2north- 1 east at top of k gate ramp |
| 2025/06/12 | Building/Structural | Slab | Passed | Kody Boswell | 4 areas of slab repair on 4th floor |
| 2025/06/12 | Building/Structural | Structural | Passed | Kody Boswell | 4 areas of slab repair on 4th floor |
| 2025/06/12 | Electrical | Ceiling Rough-in | Failed | Al Smythe | New bathrooms 4th floor section 7 and section 13 and miscellaneous 1) Panel not labeled or identified |
| 2025/05/19 | Building/Structural | Framing | Passed | Kody Boswell | Reviewed roof deck attachment to roof members for new storage room, main concourse, section 9 |
| 2025/05/09 | Building/Structural | Framing | Passed | Kody Boswell | Reviewed roof framing for 1st floor storage room section 9 |
| 2025/05/01 | Plumbing | Re-Inspection | Passed | Paul Nitz | Water supply insulation new 4th floor bathrooms |
| 2025/04/24 | Plumbing | Rough-in | Cancelled | Paul Nitz | Water supply insulation new bathrooms 4th floor section 7 and 13 this inspection was entered twice |
| 2025/04/22 | Plumbing | Water Piping & Test | Passed | Paul Nitz | New 4th floor bathroom section 13 sanitary and water supply. Also heat trace section 13 and section 7 bathroom |
| 2025/04/22 | Plumbing | Stack Piping & Test | Passed | Paul Nitz | New 4th floor bathroom section 13 sanitary and water supply. Also heat trace section 13 and section 7 bathroom |
| 2025/04/21 | Building/Structural | Framing | Passed | Kody Boswell | Reviewed roof framing and roof deck attachment to structure for new bathroom 4th floor section 13 |
| 2025/04/10 | Building/Structural | Framing | Passed | Paul Nitz | Screw down inspection for decking bathroom section 7 on the 4th floor |
| 2025/04/03 | Building/Structural | Framing | Passed | Kody Boswell | Reviewed roof framing for the new north bathroom, section 7, upper concourse. Items noted in failed inspection on 4/1/2025 have been corrected and/or addressed. |
| 2025/04/03 | Plumbing | Water Piping & Test | Passed | Paul Nitz | Re Inspection new bathroom north side 4 th floor section 7 |
| 2025/04/03 | Plumbing | Rough-in | Passed | Paul Nitz | Re Inspection new bathroom north side 4 th floor section 7 |
| 2025/04/03 | Plumbing | Stack Piping & Test | Passed | Paul Nitz | Re Inspection new bathroom north side 4 th floor section 7 |
| 2025/04/02 | Plumbing | Water Piping & Test | Failed | Paul Nitz | North new bathroom 4th floor section 7 1) Vent not supported |
| 2025/04/02 | Plumbing | Rough-in | Failed | Paul Nitz | North new bathroom 4th floor section 7 1) not holding water |
| 2025/04/02 | Plumbing | Stack Piping & Test | Failed | Paul Nitz | North new bathroom 4th floor section 7 1) not holding water and vent not supported |
| 2025/04/01 | Building/Structural | Framing | Failed | Kody Boswell | Reviewed framing new north bathroom 4th floor section 7. The following items need to be addressed/corrected: 1) Simpson clips were not used as shown in detail 5/S7.01. Contractor to verify steel angles area acceptable connections in lieu of Simpson clips with EOR or install Simpson clips. 2) Holes in angle connections along the front wall (detail 6/S7.01) and back wall appeared oversized for the screws being used for connection of angle to LG roof joists. Washers must be installed. 3) Blocking between the end joists and exterior CMU walls was not installed. Blocking must be installed. Items above were discussed with the Contractor prior to FSU BCA leaving the site. Once items are addressed, a re-inspection may be scheduled. Item 1 was addressed by the EOR with acceptance via email. Email filed in Transmittals-correspondence folder. Items 2 and 3 were resolved via re-inspection on 4/2/2025 |
| 2025/03/27 | Building/Structural | Masonry | Passed | Kody Boswell | Reviewed reinforcing steel for masonry walls for ne bathroom 4th floor section 13, final lift |
| 2025/03/24 | Building/Structural | Masonry | Passed | Kody Boswell | Reviewed reinnforcing steel for 4th floor section 13 new bathroom rebar prior to grout installation, 2nd lift |
| 2025/03/17 | Building/Structural | Masonry | Conditional | Kody Boswell | New bathroom section 13 on 4th floor 1st lift grout rebar. FSU BCA arrived on site and the Subcontractor had grouted most of the walls, so FSU BCA was not able to review. Contractor stated the Threshold Inspector (TI) had reviewed and passed the reinforcing. Result is conditional pending verification of the TI's approval. FSU BCA contacted TI via email and is awaiting a response. |
| 2025/03/13 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for the elevated slab infill on 4th level, section 13 |
| 2025/03/04 | Building/Structural | Masonry | Passed | Kody Boswell | Reviewed reinforcing steel for the top put lift of new bathroom 4th floor section 7 |
| 2025/02/27 | Building/Structural | Masonry | Passed | Kody Boswell | Re inspection for header rebar for new bathroom section 7 |
| 2025/02/26 | Building/Structural | Masonry | Conditional | Kody Boswell | Reviewed reinforcing steel for the 2nd lift of the new bathroom walls, 4th floor, section 7. Reinforcing steel was in compliance with the structural drawings except for the east wall. The horizontal reinforcing header for the door opening on the east wall did not have proper bearing over jamb reinforcing. This was discussed with the contractor while on site and must be corrected and called in for re-inspection. Contractor may proceed with grouting the north, south, and west walls. |
| 2025/02/18 | Building/Structural | Masonry | Passed | Rocky Wilde | New north bathroom 4th floor 1st lift of grout |
| 2025/02/18 | Electrical | Wall Rough-in | Passed | Rocky Wilde | New north bathroom 4th floor 1st lift of grout 4 in wall boxes |
| 2025/01/29 | Plumbing | Final Plumbing | Passed | Paul Nitz | |
| 2025/01/16 | Plumbing | Storm Piping & Test | Failed | Paul Nitz | Smoke test 1) smoke test was good, missing multiple horizontal and vertical hangers |
| 2024/11/19 | Plumbing | Storm Piping & Test | Conditional | Paul Nitz | Discuss testing options 1) smoke detection will be allowed for the storm drain only |
| 2024/11/13 | Plumbing | Storm Piping & Test | Conditional | Paul Nitz | Storm line tie in by gate L 1st floor 1) pressure test required before final inspection |
| 2024/11/13 | Plumbing | Underground | Conditional | Paul Nitz | Storm line tie in by gate L 1st floor 1) Pressure test required before final inspection |
| 2024/10/17 | Building/Structural | Slab | Conditional | Kody Boswell | Reviewed reinforcing steel and steel decking for 2 concrete repair areas noted on sheet S2.03B (ASI-09): (1) Between grids K-L/2N-3N (2) Between grids K-L/2S-3S Result is conditional pending the WWR mesh is tied down to epoxied bars prior to concrete placement. Threshold inspector to verify. |
| 2024/08/30 | Fire Safety | Final Egress/Emergency Lights | Passed | Mary Creason | Conditional certification of occupancy for the 2024 football season - Fire extinguishers to be provided by FSU, and mounts provided by MCJV to be placed in ‘back of house’ areas adjacent to the temp concession stands. - Temporary illuminated Exit Signs to be placed in locations per the design documents. 12’ AFF. To be installed today and tomorrow. - Egress Lighting Completion - We observed the battery-power operation of the high-bay fixtures in the event of a power outage. No issues were observed. A temporary CCO is approved by Fire for the 2024 season Per Sam Sever and Jason Greisel TFD and Todd Pierce State Fire Marshal office |
| 2024/08/30 | Building/Structural | Final Building | Conditional | Kody Boswell | FSU BCA walked the site to review compliance with the contract documents in order to issue a Conditional Certificate of Occupancy for the upcoming football season. The following need to be addressed prior to the issuance of the Conditional Certificate of Occupancy: 1) Steps at 7 lower vomitories need yellow paint stripes to indicate a change in height. 2) Stair stringer connection to header channel for stairs between grids 11S-12S needs to be corrected. 3) Change in elevation exceeding 1/2" where new field slab and existing field slab at grids A/16S needs to be addressed. Contractor to install flat plate to remedy trip hazard. Per conversation with the Contractor, David Zigler, items stated above would be complete over the weekend prior to the first football game on Monday (9/2/2024) and would provide photos to FSU BCA FSU BCA received pictures addressing the items above on Saturday (8/31) |
| 2024/08/29 | Fire Safety | Final Egress/Emergency Lights | Passed | Sam Sevor | Generator transfer switch was tested and Emergency lights with State Fire Marshal, Todd --- Test Passed |
| 2024/08/19 | Electrical | Ceiling Rough-in | Passed | James Melvin | 1st floor commissary building section 9 |
| 2024/08/19 | Building/Structural | Masonry | Passed | Kody Boswell | Reviewed reinforcing steel for the 2nd lift of the bosster storage walls. Reviewed reinforcing steel for the 2nd lift of masonry walls for the booster storage room in the area between grids C-E/3N-5N. Reinforcing over door openings was corrected from prior failed inspection. |
| 2024/08/15 | Electrical | Ceiling Rough-in | Passed | James Melvin | Commissary building 1st floor section 10 |
| 2024/08/15 | Building/Structural | Masonry | Failed | Kody Boswell | Reviewed reinforcing steel for the 2nd lift of masonry walls for the booster storage room in the area between grids C-E/3N-5N. Reinforcing over door openings was not installed per detail 14 on sheet S5.21. This was discussed with the Contractor and threshold inspector. Re-inspection required after reinforcing is installed. |
| 2024/08/12 | Building/Structural | Masonry | Passed | Kody Boswell | Reviewed reinforcing steel for the first lift of masonry walls for the booster storage room in the area between grids C-E/3N-5N. |
| 2024/08/08 | Fire Safety | Fire Water Above Ground | Passed | Mary Creason | hydro test for 2 hours Start 9:01am at 222psi and End at 11:21am 224psi Passed Visual on pipe/heads inside vistors locker room/maintenance shop/equipment shop/breakroom |
| 2024/08/08 | Fire Safety | Hydro-Test | Passed | Mary Creason | hydro test for 2 hours Start 9:01am at 222psi and End at 11:21am 224psi Passed Visual on pipe/heads inside vistors locker room/maintenance shop/equipment shop/breakroom |
| 2024/07/25 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed structural steel framing for new stairs and reinforcing steel for new landings between column line 8s-18s |
| 2024/07/24 | Plumbing | Storm Piping & Test | Passed | Paul Nitz | Section 4 floor drains x 4 |
| 2024/07/24 | Building/Structural | Slab | Postponed | Kody Boswell | Stairs and landings section 12-16. Contractor contacted FSU prior to arrival on site to postpone the inspection to a later date. |
| 2024/07/24 | Building/Structural | Framing | Postponed | Kody Boswell | Stairs in section 16-12. Contractor contacted FSU prior to arrival on site to postpone the inspection to a later date. |
| 2024/07/19 | Electrical | Ground | Passed | James Melvin | notes*Building ground inspection by Gate C . Gate D was inspected a week ago *notes* |
| 2024/07/12 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for elevated slabs on the upper concourse between grids 2N-9N |
| 2024/07/11 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for the following areas of elevated slab on the upper concourse: 1) In the area between grids F-J/5S-6S 2) In the area between grids F-J/2S-3S Missing reinforcing from 7/10/2024 inspection was installed and deck was cleaned off. |
| 2024/07/11 | Building/Structural | Re-Inspection | Passed | Kody Boswell | Reviewed reinforcing steel for the following areas of elevated slab on the upper concourse: 1) In the area between grids F-J/5S-6S 2) In the area between grids F-J/2S-3S Missing reinforcing from 7/10/2024 inspection was installed and deck was cleaned off. |
| 2024/07/10 | Building/Structural | Slab | Failed | Kody Boswell | Reviewed reinforcing steel for the following areas of elevated slab on the upper concourse: 1) In the area between grids F-J/5S-6S 2) In the area between grids F-J/2S-3S There was some reinforcing that was not installed per detail 7/S6.13 and there was excessive debris in some areas. Contractor to install reinforcing steel and clean off deck. |
| 2024/07/09 | Building/Structural | Slab | Postponed | Kody Boswell | Contractor contacted FSU prior to arrival on site to cancel inspection and postpone to a later date. |
| 2024/06/27 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for the elevated slab at the upper concourse level located in the area between grids F-G/7S-19S |
| 2024/06/26 | Fire Safety | Fire Water Underground | Passed | Mary Creason | Gate K fire line underground = Hydro, visual and flush for west side HYDRO Start: 8am at 224psi Finish 10:20am at 225psi Visual DR18 Flush - passed |
| 2024/06/26 | Building/Structural | ADA | Passed | Kody Boswell | Reviewed 1st floor ramps for compliance with FBC. Ramp slopes were within standards set by FBC. Connor Ross was present during the walk through. |
| 2024/06/26 | Fire Safety | Fire Water Underground | Passed | Mary Creason | Gate K, J, L and section 11: completed today - HYDRO, Visual and Flush Paperwork completed |
| 2024/06/26 | Building/Structural | Slab | Postponed | Kody Boswell | 4th floor deck columns 7 south- 19s Contractor contacted FSU BCA prior to arriving on site to cancel and postpone inspection. Contractor will reschedule for another date. |
| 2024/06/26 | Fire Safety | Fire Water Underground | Passed | Mary Creason | Section 11 fire line underground = new fire riser line : flush conducted |
| 2024/06/26 | Fire Safety | Final Fire Safety | Passed | Mary Creason | Gate K fire line underground = EAST SIDE: Hydro, visual and Flush HYDRO Start at 8:10am 225psi Finished 10:25am 226psi Visual DR18 pipe Flush - passed |
| 2024/06/21 | Plumbing | Rough-in | Passed | Dwayne Mahony | |
| 2024/06/17 | Plumbing | Rough-in | Passed | Paul Nitz | sections 14-13 and 16-15 only |
| 2024/06/12 | Plumbing | Rough-in | Failed | Paul Nitz | min slope not met on storm drain fbc p1106.2 |
| 2024/06/12 | Building/Structural | Slab | Passed | Paul Nitz | N side 4th floor elevated slab |
| 2024/06/10 | Plumbing | Rough-in | NOT READY | Paul Nitz | |
| 2024/06/05 | Plumbing | Rough-in | Passed | Paul Nitz | |
| 2024/06/05 | Building/Structural | Masonry | Passed | Kody Boswell | Reviewed reinforcing steel for new masonry walls located B-C/1E-2S |
| 2024/06/03 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for the ramp and stair footer in the area between grids B-E/8S-9S |
| 2024/05/31 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for the slab on grade ramp located between grids A-C/5S-6S |
| 2024/05/29 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for several ramps (slab on grade) |
| 2024/05/28 | Plumbing | Underground | Passed | Paul Nitz | Section 12/13 |
| 2024/05/24 | Building/Structural | Slab | Passed | Kody Boswell | Reinforcing steel for ramp slab on grade. Inspection deferred to threshold inspector. See correspondence folder for photos from Contractor. |
| 2024/05/23 | Plumbing | Rough-in | Passed | Neely Lewis | 1 floor inlet in lower level ramp |
| 2024/05/23 | Building/Structural | Slab | Passed | Kody Boswell | |
| 2024/05/22 | Building/Structural | Framing | Kody Boswell | Meeting held by the Contractor of procedures for weld inspections. FSU BCA met the Contractor, Testing Agency and Threshold Inspector in the field to discuss welding inspections. | |
| 2024/05/22 | Plumbing | Rough-in | Passed | Paul Nitz | |
| 2024/05/21 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for the following slab on grade ramps: 1) Between grids A-C/2N-3N 2) Between grids A-C/8N-9N 3) Between grids A-C/11N-12N |
| 2024/05/17 | Fire Safety | Hydro-Test | Passed | Mary Creason | test started at 7:45am at 215psi and stopped at 10:10am at 215psi. Passed test. |
| 2024/05/17 | Fire Safety | Fire Water Underground | Passed | Mary Creason | Visual passed, hydro passed and flush passed |
| 2024/05/16 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel and steel deck attachment for a portion of the slab on deck located in the area between grids A-B/7S-16S. |
| 2024/05/15 | Plumbing | Rough-in | Passed | Paul Nitz | check slope on ramp 9/10 at next inspection |
| 2024/05/15 | Plumbing | Underground | Passed | Paul Nitz | check slope on ramp 9/10 at next inspection |
| 2024/05/13 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for the following slab on grade ramps: 1) In the area between grids A-C/5N-6N 2) In the area between grids A-C/8N-9N |
| 2024/05/13 | Plumbing | Rough-in | NOT READY | Neely Lewis | |
| 2024/05/13 | Plumbing | Underground | NOT READY | Neely Lewis | |
| 2024/05/09 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel and steel deck attachment for a portion of the slab on deck located in the area between grids A-B/7N-7S. |
| 2024/05/06 | Building/Structural | Slab | Passed | Dwayne Mahony | Excess foam plastic is to be removed, T.I. will verify. |
| 2024/05/03 | Plumbing | Rough-in | Passed | Dwayne Mahony | Approved south end of grandstand lowest level, 7 area drains, and two lower vomitory ramps. |
| 2024/05/01 | Plumbing | Rough-in | Passed | Neely Lewis | partial only. |
| 2024/04/30 | Building/Structural | Footing | Passed | Kody Boswell | Reviewed reinforcing steel for a stair footing located in the area between grids B-C/17S-18S |
| 2024/04/30 | Building/Structural | Slab | Passed | Kody Boswell | Reviewed reinforcing steel for 2 slab on grade areas that were removed to install underground pipe. Reinforcing consisted of steel doweled into existing concrete at 2'-0" spacing along with WWR. |
| 2024/04/25 | Plumbing | Storm Piping & Test | Passed | Neely Lewis | |
| 2024/04/10 | Building/Structural | Footing | Passed | Kody Boswell | Reviewed reinforcing steel for a wall footing for the north wall at the visitor's locker room |
| 2024/04/02 | Building/Structural | Wall/Ceiling | Passed | Kody Boswell | Reviewed reinforcing steel for walls located along grids 14S, 15S and 16S |
| 2024/03/28 | Building/Structural | Wall/Ceiling | Passed | Kody Boswell | Reviewed reinforcing steel for walls along grids 10S, 11S, 12S and 13S. |
| 2024/03/26 | Building/Structural | Footing | Passed | Kody Boswell | Reviewed reinforcing steel for the following: - Grade beam along grid 16N - Walls along grids 8S, 9S, 14N and 15N |
| 2024/03/21 | Building/Structural | Wall/Ceiling | Passed | Kody Boswell | Reviewed reinforcing steel for walls along grids 2S, 3S, 4S, 5S, 6S and 7S |
| 2024/03/18 | Building/Structural | Wall/Ceiling | Passed | Kody Boswell | Reviewed reinforcing steel for walls along grids 2N and 1E. |
| 2024/03/15 | Building/Structural | Footing | Passed | Kody Boswell | Reviewed reinforcing steel for the following grade beams (GB) and walls: - GBs along grids 11S, 12S, 13S, 14S, 15S and 16S - Walls along grids 3N, 4N, 5N and 6N |
| 2024/03/13 | Building/Structural | Footing | Passed | Kody Boswell | Reviewed reinforcing steel for grade beams along grids 2S thru 10S. |
| 2024/03/11 | Building/Structural | Footing | Passed | Dwayne Mahony | |
| 2024/03/07 | Building/Structural | Footing | Postponed | Kody Boswell | Contractor contacted FSU to postpone the inspection to a later date. |
| 2024/03/06 | Building/Structural | Cast in Place Wall | Passed | Kody Boswell | Reviewed reinforcing steel for walls on top of grade beams located along grids 7N, 8N, 9N ,10N, 11N, 12N, 13N, 14N, 15N and the wall in the area between grids A-B/7N-16N. The deficiencies noted on 3/4/24 inspection were corrected. |
| 2024/03/05 | Building/Structural | Cast in Place Wall | Postponed | Kody Boswell | Contractor contacted FSU to postpone the inspection to a later date due to weather. |
| 2024/03/04 | Building/Structural | Cast in Place Wall | Failed | Kody Boswell | Reviewed reinforcing steel for walls on top of grade beams located along grids 7N, 8N, 9N ,10N, 11N, 12N, 13N, 14N, 15N and the wall in the area between grids A-B/7N-16N. There were several missing embeds at expansion joint locations and there was insufficient development length for #7 bars at multiple locations. Contractor to reschedule inspection after corrections are made. |
| 2024/03/01 | Building/Structural | Footing | Passed | Kody Boswell | Reviewed reinforcing steel for grade beams along grids 1E, 2N, 3N, 4N, and 5N. The deficiencies noted on the 2/29/24 inspection were corrected. |
| 2024/02/29 | Building/Structural | Footing | Failed | Kody Boswell | Reviewed reinforcing steel for grade beams along grids 2N, 3N, 4N, and 5N. Each of these grade beams were stepped and were supposed to be reinforced per detail 4/S5.01. Additional reinforcement called out in the detail going from top steel of top portion of grade beam to bottom steel of bottom portion of grade beam was not placed correctly. Also, the last stirrup located closest to the step did not encase the top steel of the bottom portion of grade beam. |
| 2024/02/27 | Building/Structural | Wall/Ceiling | Passed | Dwayne Mahony | |
| 2024/02/27 | Building/Structural | Footing | Passed | Dwayne Mahony | |
| 2024/02/23 | Building/Structural | Footing | Passed | Dwayne Mahony | |
| 2024/02/22 | Building/Structural | Footing | Failed | Kody Boswell | Reviewed reinforcing steel for grade beams located along grids 6N, 7N, 8N, 9N and 10N. Reinforcing steel at the field side was not in place per detail 7/S5.01. This was discussed with the Contractor. Contractor to contact EOR for direction due to unforeseen conditions. An RFI will be generated. |
| 2024/02/15 | Building/Structural | Footing | Postponed | Kody Boswell | Contractor contacted FSU to postpone grade beam reinforcing steel inspection to a later date. (KB) |
| 2024/02/14 | Building/Structural | Footing | Conditional | Kody Boswell | Reviewed reinforcing steel for grade beams at the lower concourse located between gridlines 15N, 14N, 13N and 12N. Where new grade beams tied to existing concrete columns there was insufficient longitudinal steel length and spacing between existing concrete face and new reinforcing ties. Per the EOR the first new reinforcing tie should be 2" to 3" off of existing concrete. This was not the case for each side of the 4 grade beams reviewed. Contractor to fix reinforcing steel prior to concrete placement. BNI (threshold) to verify reinforcing is corrected prior to concrete placement. (KB) |
| 2024/02/09 | Building/Structural | Footing | Postponed | Kody Boswell | Contractor contacted FSU to cancel today's inspection and postpone to a later date. Inspection request was for grade beam reincorcing steel. (KB) |
| 2024/02/08 | Building/Structural | Footing | Postponed | Kody Boswell | Contractor contacted FSU to cancel today's inspection and postpone to a later date. Inspection request was for grade beam reincorcing steel. (KB) |
| Building/Structural | Slab | Cancelled | Kody Boswell | Structual slab 4th section 13 column 10s line k. Contactor contacted FSU BCA on 3/7/25 to cancel inspection. | |
| Plumbing | Water Piping & Test | Postponed | Paul Nitz | Water supply new bathrooms section 7 and 13 4th floor | |
| Plumbing | Specialty Piping | Postponed | Paul Nitz | Cold water hot tie in for new bathrooms at section 7 and 13 One side to occur at 9 and the other one at 10 |

BCA Project #: 23-03455- Doak Campbell - East Stands Improvements Phase I
| Inspection Date | Discipline | Type | Result | Inspector | Comments |
| 2025/07/28 | Building/Structural | Framing | Passed | Kody Boswell | Reviewed LG framing for new ceilings for elevator machine rooms at gate A and M |
| 2025/07/28 | Building/Structural | Insulation | Passed | Kody Boswell | Reviewed insulation for ceilings for elevator machine rooms at gate A and M |
| 2025/04/24 | Plumbing | Specialty Piping | Failed | Paul Nitz | I would like to reschedule the insulation inspection to 2;30 for the new 4th floor bathrooms 1) plans call for 1'' elastomeric insulation on all supply lines 2) trap primers are bot installed |
| 2025/03/27 | Building/Structural | Masonry | NOT READY | Paul Nitz | Final lift new s bathroom 4th floor section 13 |
| 2025/03/11 | Building/Structural | Slab | NOT READY | Kody Boswell | FSU BCA arrived on site and was informed by the Subcontractor that the elevated slab reinforcing steel was not ready for inspection. FSU BCA then left the site. |
| 2025/01/15 | Plumbing | Storm Piping & Test | Failed | Paul Nitz | Smoke test |
| 2025/01/07 | Plumbing | Storm Piping & Test | NOT READY | Paul Nitz | Smoke test |
| 2024/12/16 | Building/Structural | Slab | Passed | Kody Boswell | New Plumbing drains section 5 on the 4th floor rebar |
| 2024/08/30 | Fire Safety | Final Fire Safety | Passed | Mary Creason | Temporary CCO is approved for the 2024 season by Fire. Sam Sever, Fire Manaager FSU, Jason Griisel TFD, and Todd Perce, State Fire Marshal office conducted a walk thru on 8/27/2024 and conditions were good. |
| 2024/08/27 | Electrical | Ceiling Rough-in | Passed | James Melvin | Visitors locker room |
| 2024/08/27 | Building/Structural | Other | Conditional | Paul Nitz | Compliance for football game 1) edge protection required on ramps fbc a405.9 2) protruding objects need to be protected fbc a307.0 |
| 2024/08/23 | Failed | Paul Nitz | Preliminary inspection for compliance in preparation for football game 1) ADA 303.2 vertical change on third floor 2)deburring hand rails 2) ADA 405.9 Edge protection on ground level | ||
| 2024/08/23 | Building/Structural | ADA | Failed | Paul Nitz | Preliminary inspection for compliance in preparation for football game 1) ADA 303.2 vertical change on third floor 2)deburring hand rails 2) ADA 405.9 Edge protection on ground leve |
| 2024/08/22 | Electrical | Ceiling Rough-in | Passed | James Melvin | Commissary building 1st floor section 9 |
| 2024/08/21 | Building/Structural | Sheetrock | Passed | Paul Nitz | Screw inspection visitors locker room |
| 2024/08/21 | Building/Structural | Insulation | Passed | Paul Nitz | Commisary building 1st floor section 9 |
| 2024/08/21 | Building/Structural | Roofing | Passed | Paul Nitz | Commisary building 1st floor section 9 |
| 2024/08/20 | Plumbing | Underground | Passed | Paul Nitz | Storm line tie in by gate J |
| 2024/08/20 | Building/Structural | Wall/Ceiling | Passed | Paul Nitz | Locker room bulkhead framing |
| 2024/08/02 | Building/Structural | Framing | Passed | Paul Nitz | Drywall framing in visitors locker room section 13/14 |
| 2024/08/02 | Building/Structural | Slab | Passed | Paul Nitz | Plumbing repair at existing ramp at section 4 (column 19n- 16n) 1st floor |
| 2024/08/02 | Plumbing | Rough-in | Passed | Paul Nitz | Plumbing repair at existing ramp at section 4 (column 19n- 16n) 1st floor |
| 2024/07/11 | Electrical | Ground | Passed | James Melvin | Ground rods for building steel 1) Al Smythe performed the inspection, it was from gate D to the first elevatoer shaft |
| 2024/04/29 | Fire Safety | Fire Water Underground | Passed | Mary Creason | Hydro and visual of piping, tracer line, bulimous paint and restraints on line into sprinkler riser room. Hydro start 810am 220psi and finished at 1020am at 220psi. Passed |
| 2024/04/29 | Fire Safety | System Flush | Passed | Mary Creason | UG near gate J - flushed - approved |
| 2024/04/25 | Electrical | Panel/Feeder | Passed | Dwayne Mahony | |
| 2024/04/25 | Fire Safety | Hydro-Test | Passed | Mary Creason | Visual and hydro of pipe passed. Hydro start 8:10am and ended 10:10am 205 psi Pipe is located right next to J gate. (see shop drawings for exact location) |
| 2024/04/25 | Fire Safety | Fire Water Underground | Passed | Mary Creason | Visual and hydro on UG piping at gate J. Hydro start at 8:10am at 205psi and end 10:10am at 2:05psi (See shop drawings for exact location) |
| 2024/01/24 | Electrical | Ceiling Rough-in | Conditional | Dwayne Mahony | Panel 94 deadfront piece is missing. Replacement of this piece is mandatory since new load is being added to this panel, per Existing Building code section 808.2. |
| 2024/01/22 | Electrical | Ceiling Rough-in | Passed | Dwayne Mahony | Inspected new lights and wiring on lower ramps. |
| Fire Safety | Hydro-Test | Postponed | Curtis Rogers | 4th floor fire suppression | |
| Electrical | Underground | Alex Masterton | Gate D , Small section of 15kva duct bank encasement Revise project to West Stands |